I just want to add to Mike's and Lamar's posts (for the Sprink seriously in
need of getting a life)- look at FIGURE A.8.16.2.4 Unacceptable Pressure
Gauge Location. I belive this is similar to a single hydrant flow test. Like
Lamar said, it is slightly less than two hydrant flow. The reason is that
more of the potential goes into kinetic energy, because the velociity where
the gage is NORMAL is higher. 
 
-----Original Message-----
From: Brian Harris [mailto:[email protected]] 
Sent: Wednesday, April 06, 2011 8:50 AM
To: [email protected]
Subject: Flow Test

I swear I once read that a single hydrant flow test was acceptable, maybe in
limited instances, but I can't seem to find anything on it. Any ideas?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17210)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to