That's not my option guys. We were hired to do two things,  relocate heads
for the new wall and add two heads in a concealed space. The g.c. knowingly
blocked it in and sealed it off with no intentions for further actions on
his or our part.

The only thing I can do is rationalize reasonably if possible why it is ok
as is or call the fire marshall as a whistle blower.

That is an easy decision if you are not worried about losing the inspection
contract or being black listed by the general.

So am I grasping for a legal straw? Absolutely. If those on the 13 commitee
and the majority of the rest believe it is too much of a stretch,  then I
will play whistle blower.......we do NOT want to leave it unjustifyably
wrong.
Greg
On Apr 9, 2011 10:28 AM, "Thom" <[email protected]> wrote:
> Then I'd say have the GC drywall it and mmake it a concealed
Non-combustible
> space. Or just blow it full of insul.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg
McGahan
> Sent: Friday, April 08, 2011 3:19 PM
> To: [email protected]
> Subject: Re: ENCLOSED COMBUSTIBLE STAIRS
>
> No, it is not a room, it is a combustible concealed space UNDER an area
...
>
> On Fri, Apr 8, 2011 at 4:13 PM, Thom <[email protected]> wrote:
>
>> It's not truly the "Space over the small room" it is the small room.
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Greg
>> McGahan
>> Sent: Friday, April 08, 2011 2:44 PM
>> To: [email protected]
>> Subject: ENCLOSED COMBUSTIBLE STAIRS
>>
>> We were hired to put 2 heads under a new combustible set of stairs that
>> were
>> added as an emergency egress in an existing LH building. The GC "forgot"
>> and
>> enclosed the stairs - space approximately 3-6 x 18' long - and finished
> the
>> space. We still have to relocate a couple of heads in an adjacent area so
>> we
>> are not completely free of any obligations there. Note that this space is
>> under a one floor stair and contains NOTHING, no wires, pipes, ducts, etc
>> except the framing.
>>
>> Question: Is there any chance this would even be in the same ballpark as
>> the
>> exception in chapter 8.15.1.2.9 for spaces over isolated small
>> rooms.....Since a permit was not required on this project, the AHJ does
> not
>> know about it and the only question is morally how hard we push this
>> situation.
>>
>> Thanks for your thoughts.
>> Greg
>>
>> --
>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)