I would use CMU and fire stopping. I have always wondered why Architects and Engineers require a sleeve (usually pipe) around another pipe (sprinkler pipe), specify that the space between the sprinkler pipe and the sleeve pipe must be filled with fire stop and not require the same fire stopping between the sleeve pipe and the CMU, or sheetrock, or concrete? The only reason to use a sleeve is to keep wet concrete from filling the space so core drilling isn't necessary.
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Friday, June 03, 2011 6:57 AM To: [email protected] Subject: pipe sleeves We have a job with existing pipe that the spec is requiring sleeves for all new block walls. There will be plenty of existing 1" and 1 1/4" pipe penetrating these new walls. What is the best way to sleeve existing small pipe? Thanks, Dewayne Martinez Design Build Fire Protection New Berlin, WI _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)