I didn't realize it was for a seismic zone which we are not.
Thanks for the clarification.
Dewayne 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
Sent: Monday, July 11, 2011 9:22 AM
To: [email protected]
Subject: RE: Pipe Sleeves

The "Hole" question has two parts.
1: Is there a "Seismic" requirement?
2: If there is no seismic requirement, is there some other requirement
by "Spec." or local code?

If the answer to question (1) is yes, the 8" sleeve or core is an
appropriate alternative to Flex couplings.
If the answer to (1) is "NO!" but (2) is yes, then meet the requirements
as stated in the requirement. (Size of core {If allowed} or sleeve
should be spelled out, if not you only need a "Hole" large enough for
the pipe to fit thru.
If the answer to both (1) and (2) is no, then no sleeve or core is
required.
I've seen many contractors just chop a hole in a block wall with a
hammer, and patch it back around their pipe with Sakrete. (I'm not
recommending that, but it happens and is "legal".)

Just some thoughts on sleeve's in general, and that should include core
drilled hole's as well.

Sleeve's / core's serve many purposes, but some of the original reasons
they became part of the "Standard Practice" for all mechanical trades
was that they provide for differential expansion, settling of
structures, seismic relief, vibration transmission, and ease of
repair/replacement.

Think of steam lines that expand and contract, passing thru walls. If
they are "cemented" in place, the wall either will move, the pipe will
deflect, or the joint between the two will fail. All of these can have
bad consequences. Steam is probably the most severe example, but the
same thing occurs with most mechanical systems. HW, CW, Condensate,
steam, refrigeration and yes to a lesser extent FP.

Nice 95'F day, you fill a FP system with 55'F water. Pipe contracts.
Since you're not doing anything to keep the water at 55'F as it
equalizes with the ambient temp. it expands. Same thing happens with
ambient temp. change for the seasons. A warehouse may be 100'F at the
roof in the summer, but only maintained at 50'F in winter. So even our
"Static" system "MOVES" with Temperature. It can transmit vibration. And
it's much easier, and less costly to replace a pipe section passing thru
a sleeve/core than one "cemented" in place.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Monday, July 11, 2011 4:53 AM
To: [email protected]
Subject: RE: Pipe Sleeves

I know I am late on this one but I have to know.  My fitters commonly
core a 6in hole in the stair landing for 4in pipe when running
standpipes.  It looks like we should be coring a 8in hole per 9.3.4.2.
Am I reading this correct?  
Thanks,
Dewayne


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to