Check with the architect or structural engineer. Notwithstanding sleeving to comply with seismic or thru penetration fire stopping requirements a sleeve acts as a lintel transferring a load around the nonstructural item. The IBC provides the following, specifically an opening wider than 12 inches.
2009 IBC 2104.1.4 Chases and recesses. Chases and recesses shall be constructed as masonry units are laid. Masonry directly above chases or recesses wider than 12 inches (305 mm) shall be supported on lintels. 2104.1.5 Lintels. The design for lintels shall be in accordance with the masonry design provisions of either Section 2107 or 2108. 2107.1 General. The design of masonry structures using allowable stress design shall comply with Section 2106 and the requirements of Chapters 1 and 2 of TMS 402/ACI 530/ASCE 5 except as modified by Sections 2107.2 through 2107.5. 2108.1 General. The design of masonry structures using strength design shall comply with Section 2106 and the requirements of Chapters 1 and 3 of TMS 402/ACI 530/ASCE 5, except as modified by Sections 2108.2 through 2108.3. Hope this helps, John Drucker, CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Fire Marshals Office Borough of Red Bank, NJ Not the official position of any agency, association, committee or otherwise. Obtain required applications, permits, inspections and approvals from Authority(s) Having Jurisdiction. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Thursday, July 07, 2011 5:29 PM To: [email protected] Subject: RE: Pipe Sleeves Thank you, I even checked 2006 IBC and all I could find was section 711 / 712 which was talking about rated walls. Thanks again. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, July 07, 2011 4:15 PM To: [email protected] Subject: RE: Pipe Sleeves The word sleeve only appears four times in NFPA 13, 2007. 9.3.4.2 (2-times) 22.1(22) A.3.9.5.7 related to the covering over rolled paper. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Thursday, July 07, 2011 5:11 PM To: [email protected] Subject: RE: Pipe Sleeves Thank you, just wanted to make sure I wasn't overlooking anything before I argued. We have a state fire marshal that likes to see sleeves in all block/concrete walls and I had brought this up before we started the project to try and remedy it. They said they would be willing to look into the requirements, instead of what they usually ask for, and admitted it may not be per code but they have always just asked for it. I expressed that 95% of the walls are not rated and it would be unnecessary. We are supposed to talk more about it tomorrow and I just wanted to be prepared. Thank you, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, July 07, 2011 4:03 PM To: [email protected] Subject: RE: Pipe Sleeves No requirement for sleeves in 13, just clearance. Not saying the architect or other entity may have a requirement for sleeves so check the specs if there are any. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Thursday, July 07, 2011 4:57 PM To: [email protected] Subject: Pipe Sleeves We have an existing school we are sprinkling. When we pass through a block wall, non-rated (smoke, fire etc.) we plan on providing clearance or a flex coupling within a foot of the wall on both sides of the wall. Does it say anywhere we have to use sleeves for block walls? We will be using Sch. 10 & 40 pipe as well as CPVC. I can't seem to find anything other than NFPA 13 - 2007 9.3.4.3 "Where clearance is provided by a pipe sleeve.." But nothing requiring one. Thank you in advance. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) ----- No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1388 / Virus Database: 1516/3749 - Release Date: 07/07/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) ----- No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1388 / Virus Database: 1516/3749 - Release Date: 07/07/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)