Most jurisdictions around here have a de-rate requirement, usually 10% or 10 
psi that they use to account for future development and seasonal fluctuations. 
We usually try to have a 10% safety margin in our calc's even if there is no 
mandate from the AHJ or the spec's.


Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Tuesday, July 19, 2011 7:19 AM
To: [email protected]
Subject: Re: Domestic Demand

11.1.4.3 does not address domestic so you can't hang your hat on it.   
It's chap 23.

Roland

On Jul 19, 2011, at 6:11 AM, Brian Harris wrote:

> I'm working on an Administration Building that has some really strange
> underground & plumbing configurations with relationship to the  
> sprinkler
> riser and it got me to thinking about domestic allowance in  
> calculations.
> I'm looking for some information that says I don't need to include  
> things
> like chilled water, water tank make-up, etc. in the hydraulic  
> calculations.
> I can't remember a situation where I've ever included things like  
> these in
> my calculations but like I said earlier the incoming water supply  
> has some
> strange requirements that got me thinking. I know 11.1.4.3 says the  
> minimum
> water supply requirement shall be for the sprinklers and hose  
> stream, is
> this enough to hang my hat on?
>
> Brian Harris, CET
> First Defense Fire Protection
> 11957 Ramah Church Road
> Huntersville, NC 28078
> Phone: 704.948.3506
> Fax: 704.948.3507
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to