Unenforceable? That is unquantifiable.   Who could determine what impact flood 
or ice conditions or FUTURE use may have and attached an actual value to it?

Leave a reasonable cushion in your calcs and don't design the system to within 
a half psi of available.  10 psi or 10% seems to be a typical cushion 
established by many AHJ's and Underwriters.  Even if it's not in the 13 
Standard, it would be something more defendable than the crystal ball 
engineering that 23.2.1.2 is expecting.   

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Tuesday, July 19, 2011 10:50 AM
To: [email protected]
Subject: RE: Domestic Demand

I believe the 2007, 23.2.1.2 is unenforceable.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, July 19, 2011 10:39 AM
To: [email protected]
Subject: RE: Domestic Demand

Bill-
What language would that be in the 07 edition? 


Brian Harris, CET
FDFP Inc.
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Tuesday, July 19, 2011 10:33 AM
To: [email protected]
Subject: RE: Domestic Demand

Interesting that the 2007 language (which was unenforceable) has been
eliminated in favor of the current 23.1.2 (which now could leave someone
open to liability).  I missed that.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, July 19, 2011 10:28 AM
To: [email protected]
Subject: RE: Domestic Demand

Roland-
I don't see anything in chapter 23 that talks about including domestic in
the calc's, what am I missing?  


Brian Harris, CET
FDFP Inc.
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Tuesday, July 19, 2011 10:19 AM
To: [email protected]
Subject: Re: Domestic Demand

11.1.4.3 does not address domestic so you can't hang your hat on it.   
It's chap 23.

Roland

On Jul 19, 2011, at 6:11 AM, Brian Harris wrote:

> I'm working on an Administration Building that has some really strange 
> underground & plumbing configurations with relationship to the 
> sprinkler riser and it got me to thinking about domestic allowance in 
> calculations.
> I'm looking for some information that says I don't need to include 
> things like chilled water, water tank make-up, etc. in the hydraulic 
> calculations.
> I can't remember a situation where I've ever included things like 
> these in my calculations but like I said earlier the incoming water 
> supply has some strange requirements that got me thinking. I know
> 11.1.4.3 says the minimum water supply requirement shall be for the 
> sprinklers and hose stream, is this enough to hang my hat on?
>
> Brian Harris, CET
> First Defense Fire Protection
> 11957 Ramah Church Road
> Huntersville, NC 28078
> Phone: 704.948.3506
> Fax: 704.948.3507
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920) 
> http://www.pctools.com/ ======= 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/ =======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to