There's a chart in 13R for calc'g domestic demand for typ plumbing, and in an 
admin bldg you've got process water?
I believe if you run 6" UG in, you don't need to acct for anything but AS+ 
combined hose.

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Tuesday, July 19, 2011 1:09 PM
To: [email protected]
Subject: RE: Domestic Demand

Keep in mind, a flow test performed during normal working conditions factors in 
a significant amount of domestic demand.  Remember, the static pressure taken 
is actually a residual pressure of the domestic supply.  But just to clarify, I 
am not saying a flow test takes into account industrial supplies or other 
seasonal fluctuations.  Because these fluctuations can be too hard to estimate, 
many jurisdictions require the water supply test to be adjusted to Low 
Hydraulic Gradient or require safety factors for such fluctuations.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Rahe Loftin [mailto:[email protected]]
Sent: Tuesday, July 19, 2011 12:45 PM
To: [email protected]
Subject: Re: Domestic Demand

Roland, that is correct.  The only information available in regard to 
calculation of a sprinkler system water supply that includes the domestic 
demand is in the Annex A.23.1.3.2 and A.23.2.1.  Note the connections of the 
domestic system to the fire protection system in Annex B.1, Figure B.1.

For a new building, it would be very difficult, if not impossible, to determine 
the domestic demand.  However, for an existing building, it is easier if you 
are just concerned with the domestic demand of the building.

I would assume that it would be beyond the capability for the code to be able 
to provide formulation for the domestic demand as it varies over an extreme 
range depending on the geography.

A fudge factor allowance could be incorporated into the code, but it would just 
be a feel good factor without much practical help.


On Tue, Jul 19, 2011 at 10:35 AM, Roland Huggins <[email protected]
> wrote:

> look in the Annex.  IT tells you when you have to include the domestic 
> demand.  NOT A PEEP ABOUT HOW.  This HOW issue will be pointed out to 
> the TC again at the ROC meeting.  Will I be seeing a Comment on it from you?
>  Cut-off date is Aug 30.
>
> Roland
>
> On Jul 19, 2011, at 7:27 AM, Brian Harris wrote:
>
>  Roland-
>> I don't see anything in chapter 23 that talks about including 
>> domestic in the calc's, what am I missing?
>>
>>
>> Brian Harris, CET
>> FDFP Inc.
>>
>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum-request@** 
> firesprinkler.org <to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



--
Rahe Loftin, PE
Fire Protection Engineer (AHJ)
Design & Construction 7PCE

817-371-3102
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to