Thanks guys for the help, much appreciated.
Brian Harris, CET FDFP Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Rahe Loftin Sent: Tuesday, July 19, 2011 12:45 PM To: [email protected] Subject: Re: Domestic Demand Roland, that is correct. The only information available in regard to calculation of a sprinkler system water supply that includes the domestic demand is in the Annex A.23.1.3.2 and A.23.2.1. Note the connections of the domestic system to the fire protection system in Annex B.1, Figure B.1. For a new building, it would be very difficult, if not impossible, to determine the domestic demand. However, for an existing building, it is easier if you are just concerned with the domestic demand of the building. I would assume that it would be beyond the capability for the code to be able to provide formulation for the domestic demand as it varies over an extreme range depending on the geography. A fudge factor allowance could be incorporated into the code, but it would just be a feel good factor without much practical help. On Tue, Jul 19, 2011 at 10:35 AM, Roland Huggins <[email protected] > wrote: > look in the Annex. IT tells you when you have to include the domestic > demand. NOT A PEEP ABOUT HOW. This HOW issue will be pointed out to > the TC again at the ROC meeting. Will I be seeing a Comment on it from you? > Cut-off date is Aug 30. > > Roland > > On Jul 19, 2011, at 7:27 AM, Brian Harris wrote: > > Roland- >> I don't see anything in chapter 23 that talks about including >> domestic in the calc's, what am I missing? >> >> >> Brian Harris, CET >> FDFP Inc. >> > > ______________________________**_________________ > Sprinklerforum mailing list > Sprinklerforum@firesprinkler.**org <[email protected]> > http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum< > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:Sprinklerforum-request@** > firesprinkler.org <to%[email protected]> > (Put the word unsubscribe in the subject field) > -- Rahe Loftin, PE Fire Protection Engineer (AHJ) Design & Construction 7PCE 817-371-3102 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920) http://www.pctools.com/ ======= ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)