There are some folks who approximate Pitot pressures by taking a gauge reading 
off of one ear of the hydrant while flowing the other. I haven't played with 
this to see how accurate it would be. I think it would be slightly optimistic 
to convert residual pressure off the same flowing hydrant to velocity pressure; 
conversely, you may be conservative if you assume the residual pressure at that 
hydrant is equal to the measured velocity pressure.

Mark A. Sornsin, PE | Fire Protection Engineer
Ulteig Engineers, Inc. |Fargo, ND 
Direct:    701. 280.8591 | www.ulteig.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Friday, July 22, 2011 10:08 AM
To: [email protected]
Subject: Re: Convert pitot to actual residual??

Ron,

Ron,

Yeah figured so. I just thought that someone may have had one of those 'rule of 
thumb' thingys laying around.

Seems to me THAT should be possible, no?

I just wanted this to guestimate the design ahead of doing another test.

BTW, sorry about the double posts. I'm having an argument with me this morning.



At 10:58 AM 7/22/2011, you wrote:
>Vince,
>
>Since you don't have a residual, which is the left over energy in the 
>system measured in psi at the non-flowing hydrant, while flowing 
>through that circular orifice you're screwed and the test has to be 
>re-done. Once you have actual flow and residual you can calculate flow 
>at any residual pressure (changes with the size of orifice) or residual at any 
>flow.
>Unfortunately static minus velocity (the pitot reading) doesn't equal 
>residual. Life and understanding the world would be so much easier if 
>it ran on magic and religion instead of physics.
>
>Vince Sabolik, West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136       440 
238-4800     Fax 440 238-4876
____________________________________________________________________


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to