Ron,

Ron,

Yeah figured so. I just thought that someone may have had one of those
'rule of thumb' thingys laying around.

Seems to me THAT should be possible, no?

I just wanted this to guestimate the design ahead of doing another test.

BTW, sorry about the double posts. I'm having an argument with me this morning.



At 10:58 AM 7/22/2011, you wrote:
Vince,

Since you don't have a residual, which is the left over energy in the system
measured in psi at the non-flowing hydrant, while flowing through that
circular orifice you're screwed and the test has to be re-done. Once you
have actual flow and residual you can calculate flow at any residual
pressure (changes with the size of orifice) or residual at any flow.
Unfortunately static minus velocity (the pitot reading) doesn't equal
residual. Life and understanding the world would be so much easier if it ran
on magic and religion instead of physics.

Vince Sabolik, West Tech Fire Protection, Inc.