Local condition I think just like mine. What static are you starting from in
general? I'm never less than 50 and less than 70 is rare. I have to attend a
meeting I'm already late for but this topic is intriguing. I'll be back if
anyone cares.

On Fri, Jul 22, 2011 at 9:27 AM, Art Tiroly <[email protected]> wrote:

> From my experience the hydrant gage and the pitot gage read about the same
> with pitots of 20-40 psi.
>
>
> Arthur Tiroly
> ATCO Fire Protection Design
> Tiroly and Associates
> 216-621-8899
> 216-570-7030 Cell
> WWW.ATCOfirepro.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
> Greenman
> Sent: Friday, July 22, 2011 12:09 PM
> To: [email protected]
> Subject: Re: Convert pitot to actual residual??
>
> You have one butt open with a great deal of turbulence going around the
> corner from the standpipe to the open butt while trying to take a static
> reading from the other side of the water column about 5" opposite. Not the
> best since the original static is really the residual for the entire
> pressure zone at that moment, and the residual is now the new static cum
> residual for that same system but with another source flowing.
>
> On Fri, Jul 22, 2011 at 8:46 AM, Matt Grise <[email protected]> wrote:
>
> > My understanding is that single hydrant tests are not as accurate as
> > double hydrant flow tests. You are trying to figure out how much
> > pressure you can get from the system when it is discharging a certain
> > amount of water. If you test the flowing hydrant, I imagine the
> > pressure would read lower since the water would have a pretty high
> > velocity. (just thinking out loud there... I have not researched it)
> >
> > Matt Grisé PE*, LEED AP
> > Sales Engineer
> > Alliance Fire Protection
> > 130 w 9th Ave.
> > North Kansas City, MO 64116
> >
> > *Licensed in KS & MO
> >
> > 913.888.0647 ph
> > 913.888.0618 f
> > 913.927.0222 cell
> > www. AFPsprink.com
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Smith, Steven D.
> > (CSFD)
> > Sent: Friday, July 22, 2011 10:41 AM
> > To: [email protected]
> > Subject: RE: Convert pitot to actual residual??
> >
> > What if a pressure gauge was installed on the other outlet of  the
> > hydrant from which the water is flowed and pitot reading is taken?
> >
> > IOW, is it possible to have the test and flow hydrant one in the same?
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Vince
> > Sabolik
> > Sent: Friday, July 22, 2011 9:08 AM
> > To: [email protected]
> > Subject: Re: Convert pitot to actual residual??
> >
> > Ron,
> >
> > Ron,
> >
> > Yeah figured so. I just thought that someone may have had one of those
> > 'rule of thumb' thingys laying around.
> >
> > Seems to me THAT should be possible, no?
> >
> > I just wanted this to guestimate the design ahead of doing another test.
> >
> > BTW, sorry about the double posts. I'm having an argument with me this
> > morning.
> >
> >
> >
> > At 10:58 AM 7/22/2011, you wrote:
> > >Vince,
> > >
> > >Since you don't have a residual, which is the left over energy in the
> > system
> > >measured in psi at the non-flowing hydrant, while flowing through
> > >that circular orifice you're screwed and the test has to be re-done.
> > >Once
> > you
> > >have actual flow and residual you can calculate flow at any residual
> > >pressure (changes with the size of orifice) or residual at any flow.
> > >Unfortunately static minus velocity (the pitot reading) doesn't equal
> > >residual. Life and understanding the world would be so much easier if
> > it ran
> > >on magic and religion instead of physics.
> > >
> > >Vince Sabolik, West Tech Fire Protection, Inc.
> > 11351 Pearl Road / Strongsville, Ohio 44136       440
> > 238-4800     Fax 440 238-4876
> > ____________________________________________________________________
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to