Travis, I believe that formulae gives you the flow in gpm through a circular orifice.
Vince, Since you don't have a residual, which is the left over energy in the system measured in psi at the non-flowing hydrant, while flowing through that circular orifice you're screwed and the test has to be re-done. Once you have actual flow and residual you can calculate flow at any residual pressure (changes with the size of orifice) or residual at any flow. Unfortunately static minus velocity (the pitot reading) doesn't equal residual. Life and understanding the world would be so much easier if it ran on magic and religion instead of physics. On Fri, Jul 22, 2011 at 7:42 AM, Travis Mack, SET <[email protected]>wrote: > 29.83 x hydrant coefficient x dia^2 x pitot^0.5 > Travis Mack, SET > MFP Design, LLC > www.mfpdesign.com > > Sent on the Sprint® Now Network from my BlackBerry® > > -----Original Message----- > From: Vince Sabolik <[email protected]> > Sender: [email protected]: Fri, 22 Jul 2011 > 10:35:51 > To: <[email protected]> > Reply-To: [email protected] > Subject: Convert pitot to actual residual?? > > Forum -- > > I've come across a fire department that uses the pitot tube reading as > a residual pressure. Just curious - not thinking > real good with 95°, a twelve hour flight and > a four hour time change this week - does anyone > have a formula to estimate the actual residual > pressure at the hydrant from a pitot reading? > > Vince Sabolik, West Tech Fire Protection, Inc. > 11351 Pearl Road / Strongsville, Ohio > 44136 440 238-4800 Fax 440 238-4876 > ____________________________________________________________________ > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)