Duane, I would have a problem considering 175 sqft a small opening, especially 
when it is the entire room. If a fire started in that room, there would be no 
ceiling jet until it reached roof level. My question is this a well thought-out 
performance based option or something that somebody made up? Without additional 
information, it is tough to tell.

At 07:03 AM 7/27/2011, you wrote:
>8.14.1.2.1 is more applicable.  This section permits small openings to 
>noncombustible concealed spaces. Many people don't realize, but in many 
>scenarios, the return air grilles you see in the ceiling are not ducted.  They 
>are open tiles with decorative finishes leading directly to unsprinklered 
>noncombustible concealed spaces.  The question you have to ask yourself is 
>whether or not you consider the open mesh ceiling a small opening.  And, 
>whether the small opening verbiage applies room by room or to the ceiling as a 
>whole.
>
>Additionally, you have to ask was the original installation installed 
>prescriptively or as a performance based option?  Probably not prescriptively. 
> But, it appears that sprinklers where installed above the opening to the 
>concealed space to protect the cell and for security reasons, the sprinklers 
>were raised 5 - 6 feet.  Since the cell is rather small (175 sq. ft.), the 
>fire plume should activate the sprinklers above.  From a performance based 
>perspective, it makes sense.  
>
>The other question you must ask is: are there approved as-builts on record to 
>justify the installation??
>
>Duane Johnson, PE
>Program Manager
>Division of the Fire Marshal (Support Contractor)
>Office of Research Services 
>National Institutes of Health 
>301-496-0487
>
>"Protecting Science - One Sprinkler at a Time"
>
>
>-----Original Message-----
>From: Todd Williams [mailto:[email protected]] 
>Sent: Tuesday, July 26, 2011 11:13 AM
>To: [email protected]
>Subject: Re: Concealed Space?
>
>Could you apply NFPA 13 (2002) section 8.14.1.5? (or the newer equivalent)
>
>
>At 09:45 AM 7/26/2011, you wrote:
>>Okay here is the situation. I have a Medical/Dental Facility which is part 
>>of a prison complex. The building is a noncombustible Butler type building 
>>approx. 6,200 sq. ft. in area. Ceilings are a combination of suspended 
>>ceiling tile and drywall. Walls are metal studs and drywall. Pretty 
>>straightforward so far. However they have a Detainee Holding Cell which is 
>>approx. 175 sq. ft. in area with a mesh type ceiling (almost like heavy 
>>duty chain link fence) above. From inside the cell you can look up and see 
>>the roof deck above. The walls around the cell are concrete block and only 
>>extend about 6" above the ceiling area of the adjacent rooms. This is a 
>>holding cell only, no bed, etc. Inmates wait in this cell before being 
>>removed for examination. Sprinkler protection is installed throughout the 
>>entire drop ceiling area. No sprinkler protection at the roof deck above 
>>except for two heads over the cell. Heads are about 5'-6' above cell.  Is 
>>this acceptable? Is this space still considered a noncombustible concealed 
>>space not requiring sprinkler protection throughout? My thinking is that 
>>for this to be acceptable the walls around the cell should extend to the 
>>roof deck. 
>>
>>Matt
>>Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection 
>>l [email protected] l O +864.517.1814 l www.fluor.com
>>------------------------------------------------------------
>>The information transmitted is intended only for the person 
>>or entity to which it is addressed and may contain 
>>proprietary, business-confidential and/or privileged material.  
>>If you are not the intended recipient of this message you are 
>>hereby notified that any use, review, retransmission, dissemination, 
>>distribution, reproduction or any action taken in reliance upon 
>>this message is prohibited. If you received this in error, please 
>>contact the sender and delete the material from any computer.  
>>
>>Any views expressed in this message are those of the individual 
>>sender and may not necessarily reflect the views of the company.  
>>------------------------------------------------------------
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to