Duane, I would have a problem considering 175 sqft a small opening, especially when it is the entire room. If a fire started in that room, there would be no ceiling jet until it reached roof level. My question is this a well thought-out performance based option or something that somebody made up? Without additional information, it is tough to tell.
At 07:03 AM 7/27/2011, you wrote: >8.14.1.2.1 is more applicable. This section permits small openings to >noncombustible concealed spaces. Many people don't realize, but in many >scenarios, the return air grilles you see in the ceiling are not ducted. They >are open tiles with decorative finishes leading directly to unsprinklered >noncombustible concealed spaces. The question you have to ask yourself is >whether or not you consider the open mesh ceiling a small opening. And, >whether the small opening verbiage applies room by room or to the ceiling as a >whole. > >Additionally, you have to ask was the original installation installed >prescriptively or as a performance based option? Probably not prescriptively. > But, it appears that sprinklers where installed above the opening to the >concealed space to protect the cell and for security reasons, the sprinklers >were raised 5 - 6 feet. Since the cell is rather small (175 sq. ft.), the >fire plume should activate the sprinklers above. From a performance based >perspective, it makes sense. > >The other question you must ask is: are there approved as-builts on record to >justify the installation?? > >Duane Johnson, PE >Program Manager >Division of the Fire Marshal (Support Contractor) >Office of Research Services >National Institutes of Health >301-496-0487 > >"Protecting Science - One Sprinkler at a Time" > > >-----Original Message----- >From: Todd Williams [mailto:[email protected]] >Sent: Tuesday, July 26, 2011 11:13 AM >To: [email protected] >Subject: Re: Concealed Space? > >Could you apply NFPA 13 (2002) section 8.14.1.5? (or the newer equivalent) > > >At 09:45 AM 7/26/2011, you wrote: >>Okay here is the situation. I have a Medical/Dental Facility which is part >>of a prison complex. The building is a noncombustible Butler type building >>approx. 6,200 sq. ft. in area. Ceilings are a combination of suspended >>ceiling tile and drywall. Walls are metal studs and drywall. Pretty >>straightforward so far. However they have a Detainee Holding Cell which is >>approx. 175 sq. ft. in area with a mesh type ceiling (almost like heavy >>duty chain link fence) above. From inside the cell you can look up and see >>the roof deck above. The walls around the cell are concrete block and only >>extend about 6" above the ceiling area of the adjacent rooms. This is a >>holding cell only, no bed, etc. Inmates wait in this cell before being >>removed for examination. Sprinkler protection is installed throughout the >>entire drop ceiling area. No sprinkler protection at the roof deck above >>except for two heads over the cell. Heads are about 5'-6' above cell. Is >>this acceptable? Is this space still considered a noncombustible concealed >>space not requiring sprinkler protection throughout? My thinking is that >>for this to be acceptable the walls around the cell should extend to the >>roof deck. >> >>Matt >>Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection >>l [email protected] l O +864.517.1814 l www.fluor.com >>------------------------------------------------------------ >>The information transmitted is intended only for the person >>or entity to which it is addressed and may contain >>proprietary, business-confidential and/or privileged material. >>If you are not the intended recipient of this message you are >>hereby notified that any use, review, retransmission, dissemination, >>distribution, reproduction or any action taken in reliance upon >>this message is prohibited. If you received this in error, please >>contact the sender and delete the material from any computer. >> >>Any views expressed in this message are those of the individual >>sender and may not necessarily reflect the views of the company. >>------------------------------------------------------------ >>_______________________________________________ >>Sprinklerforum mailing list >>[email protected] >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >>For Technical Assistance, send an email to: [email protected] >> >>To Unsubscribe, send an email to:[email protected] >>(Put the word unsubscribe in the subject field) > >Todd G. Williams, PE >Fire Protection Design/Consulting >Stonington, CT >860.535.2080 >www.fpdc.com > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)