Look at NFPA 13 8.15.22.3  2010ed. 

Note that the section only says "only on one side" so I'm not sure it would 
apply to your configuration.  

Next option is "Vertical Openings" 8.15.4.


Ryan Peterson
Wayne Automatic Fire Sprinklers

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, July 27, 2011 9:06 AM
To: [email protected]
Subject: RE: Concealed Space?

Sorry but if you're referencing NFPA 13, 2002 8.14.1.2.1 I can't see how you 
would apply that to this situation.  175 sq. ft. is not a small opening like a 
return grille or access panel.

Review:  A 175 sq. ft room of noncombustible construction which is open to the 
roof deck (opening is 175sq. ft).  Adjacent rooms have ceilings.  This cell has 
no ceiling, only a fenced barrier at the top for security.  The room is open to 
the ceiling cavity of the adjacent areas.  Sprinklers are provided directly 
above this space but not in the ceiling cavity adjacent to this room.

First a concealed space is typically a non-occupied space with limited access.  
The space above the ceilings in the adjacent rooms could be considered a 
concealed space.

So I'm not seeing how the concealed space sections have applicability to the 
protection of this room.

This basic scenario has been discussed before where there are ceilings of 
different heights and are open to each other.  Typically the room has 
sprinklers at the deck as has been described and additional sprinklers are 
provided at the deck beyond the perimeter of the room into the adjacent 
concealed ceiling cavity.  Can't remember the exact chapter and verse and just 
don't have time to look it up right now.





Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Wednesday, July 27, 2011 7:04 AM
To: [email protected]
Subject: RE: Concealed Space?

8.14.1.2.1 is more applicable.  This section permits small openings to 
noncombustible concealed spaces. Many people don't realize, but in many 
scenarios, the return air grilles you see in the ceiling are not ducted.  They 
are open tiles with decorative finishes leading directly to unsprinklered 
noncombustible concealed spaces.  The question you have to ask yourself is 
whether or not you consider the open mesh ceiling a small opening.  And, 
whether the small opening verbiage applies room by room or to the ceiling as a 
whole.

Additionally, you have to ask was the original installation installed 
prescriptively or as a performance based option?  Probably not prescriptively.  
But, it appears that sprinklers where installed above the opening to the 
concealed space to protect the cell and for security reasons, the sprinklers 
were raised 5 - 6 feet.  Since the cell is rather small (175 sq. ft.), the fire 
plume should activate the sprinklers above.  From a performance based 
perspective, it makes sense.  

The other question you must ask is: are there approved as-builts on record to 
justify the installation??

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Tuesday, July 26, 2011 11:13 AM
To: [email protected]
Subject: Re: Concealed Space?

Could you apply NFPA 13 (2002) section 8.14.1.5? (or the newer equivalent)


At 09:45 AM 7/26/2011, you wrote:
>Okay here is the situation. I have a Medical/Dental Facility which is part 
>of a prison complex. The building is a noncombustible Butler type building 
>approx. 6,200 sq. ft. in area. Ceilings are a combination of suspended 
>ceiling tile and drywall. Walls are metal studs and drywall. Pretty 
>straightforward so far. However they have a Detainee Holding Cell which is 
>approx. 175 sq. ft. in area with a mesh type ceiling (almost like heavy 
>duty chain link fence) above. From inside the cell you can look up and see 
>the roof deck above. The walls around the cell are concrete block and only 
>extend about 6" above the ceiling area of the adjacent rooms. This is a 
>holding cell only, no bed, etc. Inmates wait in this cell before being 
>removed for examination. Sprinkler protection is installed throughout the 
>entire drop ceiling area. No sprinkler protection at the roof deck above 
>except for two heads over the cell. Heads are about 5'-6' above cell.  Is 
>this acceptable? Is this space still considered a noncombustible concealed 
>space not requiring sprinkler protection throughout? My thinking is that 
>for this to be acceptable the walls around the cell should extend to the 
>roof deck. 
>
>Matt
>Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection 
>l [email protected] l O +864.517.1814 l www.fluor.com
>------------------------------------------------------------
>The information transmitted is intended only for the person 
>or entity to which it is addressed and may contain 
>proprietary, business-confidential and/or privileged material.  
>If you are not the intended recipient of this message you are 
>hereby notified that any use, review, retransmission, dissemination, 
>distribution, reproduction or any action taken in reliance upon 
>this message is prohibited. If you received this in error, please 
>contact the sender and delete the material from any computer.  
>
>Any views expressed in this message are those of the individual 
>sender and may not necessarily reflect the views of the company.  
>------------------------------------------------------------
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to