The 2010 edition of NFPA's Automatic Sprinkler Systems for Residential 
Occupancies Handbook contains a lot of good commentary on this subject in its 
treatment of NFPA 13R 7.2 [Design Criteria - Outside Dwelling Unit].  If you 
don't have access to this, at least note the appendix material in A.7.2 which 
makes it clear that NFPA 13 is only partially referenced and is only for the 
specific criteria listed in 7.2 and its subsections and does not bring in any 
other rules from NFPA 13.  

It is very important to know whether the building is classified by the 
Architect [and Building Official] as Residential Occupancy or Mixed Occupancy 
because 2010 NFPA 13R 7.2.4.1 states clearly that "For a mixed occupancy, 
[...], the BUILDING shall comply with NFPA 13."  This ties in with the appendix 
material in A1.1 regarding scope which also addresses mixed occupancy.

Note also there is a separate section specifically on garages in 7.3; however, 
7.3.2 will most likely send you back to 7.2.

I'm sorry if the references aren't addressing the 2002 edition - we haven't had 
the 2002 as a minimum standard in many years [since January 26, 2007].


Respectfully,


David W. S. Blackwell, II, PE, CFPE
Engineer III
Office of State Fire Marshal
SC Department of Labor, Licensing, & Regulation, 141 Monticello Trail, 
Columbia, SC 29203
Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
Fax: 803.896.9806 [Office]
Email:   [email protected]
Website:  www.scfiremarshal.llronline.com 



Please note that you can sign up to receive automatic information on SC 
Division of Fire and Life Safety current events, policies, laws and procedures 
by visiting our Web site at:  http://www.llr.state.sc.us/firemarshal.asp

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Friday, July 29, 2011 2:57 PM
To: [email protected]; Sheila Gabler
Subject: RE: NFPA 13R Question

Sheila:

Unless there is some provision in the applicable code for exception of
sprinkler protection in this area, I believe this would fall into the
category of "areas outside of dwelling units", and is required to be
protected by NFPA 13 (as stated in 13R).   The NFPA standards don't
"require" sprinklers in areas - that's based in the applicable code - so
if the code says to sprinkler a building, you sprinkler all areas,
except where specifically allowed not to by the referenced standard.
My take would be that the applicable code requires sprinklers per 13R,
and 13R says you can exclude sprinklers in certain areas, such as
clothes closets, concealed spaces, etc.   But it doesn't contain
provisions for excluding this area, even with the fire separation. 


Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sheila
Gabler
Sent: Friday, July 29, 2011 11:50 AM
To: [email protected]
Subject: NFPA 13R Question

We have run into a situation where we are designing an NFPA 13R (2002
code) fire suppression system for a 3 storey residential building of
combustible construction where there is parking on the first storey for
7 cars that is covered by second floor suites but is otherwise open to
air.  

The parking and the suites are separated by a 1.5 hour fire separation.
The parking is intended for the residents of the building.  There is no
underground parkade.  We are located in British Columbia, Canada and do
not use the IBC but rather a provinical building code.

Does NFPA 13R require fire suppression to protect the covered parking
area? 

Thank you,
 
Sheila Gabler
HPF Engineering Ltd.
 
101-1402 McGill Road
Kamloops, BC, V2C 1L3
Ph: (250) 828-7992 
Fax:(250) 828-0984 
email: [email protected]

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to