I'd like to hear from a committee member but I'd guess that the change was
to eliminate this interpretation of needing to sprinkler the entire
unoccupied space merely because a single piece of equipment is present. I
looked for the ROP to see the justification statement but couldn't find
anything. This is a life safety code after all.

On Wed, Nov 30, 2011 at 4:49 PM, njarendt tds.net <[email protected]> wrote:

> My take is that it says at least one is over the heater it does not say
> that the rest of the space is not sprinklered.  We would require the entire
> space to be sprinklered with at least one sprinkler directly above the
> unit.
>
> Norm
>
> On Wed, Nov 30, 2011 at 4:33 PM, Smith, Steven D. (CSFD) <
> [email protected]> wrote:
>
> > In the 2002 edition 6.8.5 states "... and other concealed spaces that
> > are not used or intended for living purposes or storage and do not
> > contain fuel-fired equipment." Meaning that if fuel fired appliances are
> > located in a crawl space below the main occupancy (as an example) then
> > sprinklers are required throughout the crawl space.
> >
> > Fast forward to 2010 edition and 6.6.6.1  "When fuel fired equipment is
> > present, at least one QR intermediate temperature sprinkler shall be
> > installed above the equipment."  I read this as a crawl space that has a
> > heater (again, as an example) the entire crawl space does not need to be
> > sprinklered throughout but just above the fuel-fired appliance only.
> >
> > If I'm reading things correctly, my question is why? What changed to
> > previously require sprinklers throughout the crawl space and now just
> > over the fuel fired appliance? Or is my original assumption with the
> > 2002 ed incorrect in that the intent of that section was to protect the
> > fuel-fired appliance and not necessarily throughout the space it's
> > located?
> >
> > Note that I'm not sure when 6.6.6.1 was added as my research hasn't
> > gotten me that far. But I'm still curious.
> >
> > Thanks in advance.
> >
> > Steve
> >
> > Steven Smith, CFPS | Fire Protection Engineer II
> > Colorado Springs Fire Department | Division of the Fire Marshal
> > Division of the Fire Marshal on Facebook <http://on.fb.me/dxW5Qx>
> >
> >
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111130/1992bcd6/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Norman Arendt, CHS III, CMAS, PhD, CFEII
> President Infragard Madison Members Alliance
> Middleton Fire District Plan Reviewer and Investigator
> PCII and CVI Certified
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111130/331f4d34/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111130/c53d4802/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to