Concur with the below BUT (and its a big one), 13R is going through a
big evolution on this issue. As Steve stated, whether or not to
protect different PORTIONS of a building is a code decision. NFPA 13
and 13R historically have disagreed with this position but they are
learning that they are not at the helm for this decision.
Read the ROP and watch for the ROC after the Sept meetings.
Roland
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org
On Aug 1, 2011, at 6:54 AM, David Blackwell wrote:
The 2010 edition of NFPA's Automatic Sprinkler Systems for
Residential Occupancies Handbook contains a lot of good commentary
on this subject in its treatment of NFPA 13R 7.2 [Design Criteria -
Outside Dwelling Unit]. If you don't have access to this, at least
note the appendix material in A.7.2 which makes it clear that NFPA
13 is only partially referenced and is only for the specific
criteria listed in 7.2 and its subsections and does not bring in any
other rules from NFPA 13.
It is very important to know whether the building is classified by
the Architect [and Building Official] as Residential Occupancy or
Mixed Occupancy because 2010 NFPA 13R 7.2.4.1 states clearly that
"For a mixed occupancy, [...], the BUILDING shall comply with NFPA
13." This ties in with the appendix material in A1.1 regarding
scope which also addresses mixed occupancy.
Note also there is a separate section specifically on garages in
7.3; however, 7.3.2 will most likely send you back to 7.2.
I'm sorry if the references aren't addressing the 2002 edition - we
haven't had the 2002 as a minimum standard in many years [since
January 26, 2007].