Continued.
Similar scenario opened twenty two (22) heads. 
All of the events like this I am familiar with involved adults,  not children 
escaping.
Heads under decks,  per IFC?  I don't know.  It may be that the FF's haven't 
found those fires of note enough to ring me, or maybe they haven't happened 
yet. 
Bruce 

Sent from my Motorola ATRIX™ 4G on AT&T

-----Original message-----
From: Bruce Verhei <[email protected]>
To: [email protected]
Sent: Fri, Dec 2, 2011 04:33:34 GMT+00:00
Subject: RE: NFPA 13R Question

Fire burning up from the patio, and then progressively up the lanai's, and into 
the attic via the bird blocking happens. Along the way the sliding glass doors 
break out and fire gases enter the units on each floor. The fires I've seen 
have been controlled in the living units. Off course involvement in the attic 
is complete to separation or draft stop. The roof is totally removed and new 
trusses installed. The fire enters each unit between the bedrooms and the door. 
We've had successful escape by the sleeping residents so far, but with 
considerable smoke exposure sometimes.  
Probably the closest run was by a person on the second floor. 3/4 cord of wood 
burning on the patio. 4 heads on living entry dinette kitchen area. Residents 
got out. 4 heads on second floor. Fire investigators said it wad a close run 
thing that that male barely made it out. 3 heads (11 total) on third floor.  
One of the old PB systems. I checked.  Fire was in the remote area, 4 heads.

Another simila
Sent from my Motorola ATRIX™ 4G on AT&T

-----Original message-----
From: Steve Leyton <[email protected]>
To: [email protected]
Sent: Thu, Dec 1, 2011 17:40:00 GMT+00:00
Subject: RE: NFPA 13R Question

NFPA 13R very specifically exempts combustible concealed spaces from
protected areas in buildings to which the standard is applicable.
Concealed space provisions are widely interpreted differently, including
and especially where you have non-dwelling unit areas where there is
combustible concealed space above.   I believe it is the intent that ALL
combustible concealed spaces are exempted, including those over areas
where 13 is applied such as lobbies or service areas in mid-rise
hotel/motel occupancies.  Like 13D, 13R is a LIFE safety standard by
priority, not a property protection standard.

With that in mind, the use of a single sprinkler in the immediate
vicinity is as a sentinel or "alarm" sprinkler, to hopefully sound
waterflow if there is an incident in an attic or interstitial space.
There have been several documented roof burn-offs and horizontal fire
spread through unprotected attics in 13R buildings and there is energy
in the ICC and fire service communities to eliminate 13R or to require
sprinklers in those spaces.  The committee heard and rejected at least
one such proposal this cycle.    With all of the foregoing considered,
my take is that you install a single sprinkler only and the presence of
that sprinkler does not trigger protecting the entire concealed
compartment.

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 13D/13R Technical Committee on Residential
Sprinkler Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Wednesday, November 30, 2011 5:19 PM
To: [email protected]
Subject: Re: NFPA 13R Question

I'd like to hear from a committee member but I'd guess that the change
was
to eliminate this interpretation of needing to sprinkler the entire
unoccupied space merely because a single piece of equipment is present.
I
looked for the ROP to see the justification statement but couldn't find
anything. This is a life safety code after all.

On Wed, Nov 30, 2011 at 4:49 PM, njarendt tds.net <[email protected]>
wrote:

> My take is that it says at least one is over the heater it does not
say
> that the rest of the space is not sprinklered.  We would require the
entire
> space to be sprinklered with at least one sprinkler directly above the
> unit.
>
> Norm
>
> On Wed, Nov 30, 2011 at 4:33 PM, Smith, Steven D. (CSFD) <
> [email protected]> wrote:
>
> > In the 2002 edition 6.8.5 states "... and other concealed spaces
that
> > are not used or intended for living purposes or storage and do not
> > contain fuel-fired equipment." Meaning that if fuel fired appliances
are
> > located in a crawl space below the main occupancy (as an example)
then
> > sprinklers are required throughout the crawl space.
> >
> > Fast forward to 2010 edition and 6.6.6.1  "When fuel fired equipment
is
> > present, at least one QR intermediate temperature sprinkler shall be
> > installed above the equipment."  I read this as a crawl space that
has a
> > heater (again, as an example) the entire crawl space does not need
to be
> > sprinklered throughout but just above the fuel-fired appliance only.
> >
> > If I'm reading things correctly, my question is why? What changed to
> > previously require sprinklers throughout the crawl space and now
just
> > over the fuel fired appliance? Or is my original assumption with the
> > 2002 ed incorrect in that the intent of that section was to protect
the
> > fuel-fired appliance and not necessarily throughout the space it's
> > located?
> >
> > Note that I'm not sure when 6.6.6.1 was added as my research hasn't
> > gotten me that far. But I'm still curious.
> >
> > Thanks in advance.
> >
> > Steve
> >
> > Steven Smith, CFPS | Fire Protection Engineer II
> > Colorado Springs Fire Department | Division of the Fire Marshal
> > Division of the Fire Marshal on Facebook <http://on.fb.me/dxW5Qx>
> >
> >
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> >
>
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachm
ents/20111130/1992bcd6/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Norman Arendt, CHS III, CMAS, PhD, CFEII
> President Infragard Madison Members Alliance
> Middleton Fire District Plan Reviewer and Investigator
> PCII and CVI Certified
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
>
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachm
ents/20111130/331f4d34/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111130/c53d4802/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111201/407e92c7/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to