John's analysis is pretty much what I came up with, except we are using 8" pipe 
to a hydrant outside the school. This is a new school being constructed behind 
an existing one. I don't think a hydrant on the road would be used as most 
trucks would go in the driveway to the new location. Sounds like this would be 
OK. 


At 09:17 AM 8/24/2011, you wrote:
>Todd,
>I would first confirm the flow test data, as 46 PITOT pressure will give you
>1138 GPM.  The two GPM numbers are too close for comfort and may suggest a
>single fire hydrant flow test was used to arrive at this data.  Assuming the
>flow test data is accurate look at the following:
>Combined elevation and flow losses at 275 GPM are 30 PSI.
>The 20 PSI minimum will be at the point of connection, not at the elevation
>of the fire pump.  
>At zero gallons flowing your static at the street is 54, at pump suction
>will be (54-28) 26 PSI.
>At 275 GPM your residual at street will be 53, while at pump suction it will
>be (53-30) 23 PSI
>At 500 GPM your residual at street will be 52, while at pump suction it will
>be (52-28-6) 18 PSI.  The 6 being loss in 6" DIP at 500 GPM.
>At 750 GPM (for the one time you test the pump at 150%) the residual at
>street will be 50 PSI, while the residual at pump suction will be (50-28-13)
>9 PSI.  The 13 being loss in 6" DIP at 750 GPM.
>In no case will the residual be less than 50 at the city connection.  Baring
>any objection from the EOR, or an agent from the water purveyor who cannot
>or will not read the calcs and flow curves, you should be OK.  Remember you
>will always have a positive pressure at suction, and the worse condition is
>only at the onetime 150% pump test.
>John O'Connor
>National Fire Sprinklers, Inc.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Wednesday, August 24, 2011 7:47 AM
>To: [email protected]
>Subject: RE: Minimum pressures in water supply
>
>The 30 psi does include elevation and friction. My guess is that the inlet
>pressure of the pump would be around 16-18 psi. No, the pump house is part
>of the main structure and cannot be moved.
>
>
>At 08:31 AM 8/24/2011, you wrote:
>>Does the loss of 30 psi include the friction and the elevation loss? If
>not, then you are getting pretty close to having cavitation at the pump
>inlet and/or collapsing the supply pipe.
>>
>>Can you put the pump house lower on the hill?
>>
>>Matt Grisé PE*, LEED AP 
>>Sales Engineer 
>>Alliance Fire Protection 
>>130 w 9th Ave.
>>North Kansas City, MO 64116
>>
>>*Licensed in KS & MO 
>>
>>913.888.0647 ph 
>>913.888.0618 f 
>>913.927.0222 cell 
>>www. AFPsprink.com 
>>
>>
>>-----Original Message-----
>>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>>Sent: Wednesday, August 24, 2011 7:21 AM
>>To: [email protected]
>>Subject: Minimum pressures in water supply
>>
>>I am working on a new school project, where the building is 65 ft above the
>water supply in the road and 760 ft horizontally. The water supply is
>54-46-1130. There is a pump planned, which I have to size. The total
>pressure loss in the underground between the supply and the pump house is
>approximately 30 psi. I know the general consensus (and some water company
>requirements) is that the water pressure not be drawn down below 20 psi.  A
>500 gpm at 60 psi pump would be a good fit for this project, but the suction
>pressures at the pump would end up being below 20 psi. The supply in the
>public mains would remain above 20 (due to the elevation), but would be
>below that in the private main at the pump room. Any thought if this would
>be acceptable?
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, CT
>>860.535.2080
>>www.fpdc.com
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>-----
>No virus found in this message.
>Checked by AVG - www.avg.com
>Version: 10.0.1392 / Virus Database: 1520/3853 - Release Date: 08/23/11
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com