NFPA 101,2006 allows it.  Chapter 18 New Health Care Facilities

18.3.5.5*  Listed quick-response or listed residential sprinklers shall be used 
throughout smoke compartments containing patient sleeping rooms.  

A.18.3.5.5 The requirements for use of quick-response sprinklers intend that 
quick-response sprinklers be the predominant type of sprinkler installed in the 
smoke compartment. It is recognized, however, that quick-response sprinklers 
might not be approved for installation in all areas such as those where NFPA 
13, Standard for the Installation of Sprinkler Systems, requires sprinklers of 
the intermediate- or high-temperature classification. It is not the intent of 
the 18.3.5.5 requirements to prohibit the use of standard sprinklers in limited 
areas of a smoke compartment where intermediate- or high-temperature sprinklers 
are required.  
Where the installation of quick-response sprinklers is impracticable in patient 
sleeping room areas, appropriate equivalent protection features acceptable to 
the authority having jurisdiction should be provided. It is recognized that the 
use of quick-response sprinklers might be limited in facilities housing certain 
types of patients or by the installation limitations of quick-response 
sprinklers.  

You should also check NFPA 99.

Jack Fairchild, CFPS  |  Manager of Fire Protection and Life Safety  
|  Ballinger  |  v 215.446.0596 |   f  215.446.0597  |  833 Chestnut Street  
Suite 1400    Philadelphia, PA   19107  |  www.ballinger-ae.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Travis Mack, SET
Sent: Monday, October 31, 2011 11:58 AM
To: Matt Grise
Cc: '[email protected]'
Subject: Re: Residential Sprinkler in I-2

An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111031/03b78a21/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to