What is the occupancy?  I-2 does not necessarily parallel with NFPA 101 Health 
Care chapters.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Fairchild, Jack [mailto:[email protected]] 
Sent: Monday, October 31, 2011 12:06 PM
To: [email protected]; [email protected]
Subject: RE: Residential Sprinkler in I-2

NFPA 101,2006 allows it.  Chapter 18 New Health Care Facilities

18.3.5.5*  Listed quick-response or listed residential sprinklers shall be used 
throughout smoke compartments containing patient sleeping rooms.  

A.18.3.5.5 The requirements for use of quick-response sprinklers intend that 
quick-response sprinklers be the predominant type of sprinkler installed in the 
smoke compartment. It is recognized, however, that quick-response sprinklers 
might not be approved for installation in all areas such as those where NFPA 
13, Standard for the Installation of Sprinkler Systems, requires sprinklers of 
the intermediate- or high-temperature classification. It is not the intent of 
the 18.3.5.5 requirements to prohibit the use of standard sprinklers in limited 
areas of a smoke compartment where intermediate- or high-temperature sprinklers 
are required.  
Where the installation of quick-response sprinklers is impracticable in patient 
sleeping room areas, appropriate equivalent protection features acceptable to 
the authority having jurisdiction should be provided. It is recognized that the 
use of quick-response sprinklers might be limited in facilities housing certain 
types of patients or by the installation limitations of quick-response 
sprinklers.  

You should also check NFPA 99.

Jack Fairchild, CFPS  |  Manager of Fire Protection and Life Safety  
|  Ballinger  |  v 215.446.0596 |   f  215.446.0597  |  833 Chestnut Street  
Suite 1400    Philadelphia, PA   19107  |  www.ballinger-ae.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Travis Mack, SET
Sent: Monday, October 31, 2011 11:58 AM
To: Matt Grise
Cc: '[email protected]'
Subject: Re: Residential Sprinkler in I-2

An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111031/03b78a21/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to