2'-10" x 2'-10" closet with 9 ft ceiling. A full width and depth shelf is at 
4'-2" above the floor. AC unit sits on the shelf and water heater is below, 
there is a typical 6'-8" door on the closet . Applicable code is 2002 NFPA #13. 
The inspector is insisting that we add sprinkler beneath the shelf to cover the 
water heater because of the obstruction from the shelf supporting the AC. Of 
course it is near the end of the project and this is the first time the issue 
has been raised. We pointed out that 6.4.6.3.1 in 13R (2010) and the handbook 
says one head is enough in 400 sqft. closet. The inspector says that 13R 
doesn't apply and that 13 is blah blah blah. He is technically correct but holy 
cow 2 heads in a six square feet closet?

I thought that if I could find the ROP and ROC for what is currently 6.4.6.3.1 
in 13R that there would be something in the substantiation we could send to the 
inspector. Or do you think the inspector is right, do we need another sprinkler?


Ron Fletcher
Aero Automatic
Phoenix, AZ



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to