I have run into similar situations and a grated shelf was required.

At 12:55 PM 4/25/2012, you wrote:
>Hello RFletcher,
>
> From the way I read this the shelf blocks ALL of the space side to
>side AND front to rear in the space below the AC unit.  How does the
>Sprinkler water get to the space where the hot water heater is? 
>
>Wednesday, April 25, 2012, 10:10:03 AM, you wrote:
>
>> 2'-10" x 2'-10" closet with 9 ft ceiling. A full width and depth
>> shelf is at 4'-2" above the floor. AC unit sits on the shelf and
>> water heater is below, there is a typical 6'-8" door on the closet .
>> Applicable code is 2002 NFPA #13. The inspector is insisting that we
>> add sprinkler beneath the shelf to cover the water heater because of
>> the obstruction from the shelf supporting the AC. Of course it is
>> near the end of the project and this is the first time the issue has
>> been raised. We pointed out that 6.4.6.3.1 in 13R (2010) and the
>> handbook says one head is enough in 400 sqft. closet. The inspector
>> says that 13R doesn't apply and that 13 is blah blah blah. He is
>> technically correct but holy cow 2 heads in a six square feet closet?
>
>> I thought that if I could find the ROP and ROC for what is
>> currently 6.4.6.3.1 in 13R that there would be something in the
>> substantiation we could send to the inspector. Or do you think the
>> inspector is right, do we need another sprinkler?
>
>
>> Ron Fletcher
>> Aero Automatic
>> Phoenix, AZ
>
>
>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>> -----
>> No virus found in this message.
>> Checked by AVG - www.avg.com
>> Version: 2012.0.1913 / Virus Database: 2411/4958 - Release Date: 04/25/12
>
>
>
>
>-- 
>Best regards,
> Charles                            mailto:[email protected]
>
> Confidentiality Notice: This e-mail message, including any attachments, is
> for the sole purpose of the intended recipients and may contain confidential
> and privileged information.  Any unauthorized review, use, disclosure or
> distribution is prohibited.  If you are not the intended recipient, please 
> contact
> the sender by reply e-mail and destroy all copies of the original message.
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com