Hello RFletcher,

>From the way I read this the shelf blocks ALL of the space side to
side AND front to rear in the space below the AC unit.  How does the
Sprinkler water get to the space where the hot water heater is? 

Wednesday, April 25, 2012, 10:10:03 AM, you wrote:

> 2'-10" x 2'-10" closet with 9 ft ceiling. A full width and depth
> shelf is at 4'-2" above the floor. AC unit sits on the shelf and
> water heater is below, there is a typical 6'-8" door on the closet .
> Applicable code is 2002 NFPA #13. The inspector is insisting that we
> add sprinkler beneath the shelf to cover the water heater because of
> the obstruction from the shelf supporting the AC. Of course it is
> near the end of the project and this is the first time the issue has
> been raised. We pointed out that 6.4.6.3.1 in 13R (2010) and the
> handbook says one head is enough in 400 sqft. closet. The inspector
> says that 13R doesn't apply and that 13 is blah blah blah. He is
> technically correct but holy cow 2 heads in a six square feet closet?

> I thought that if I could find the ROP and ROC for what is
> currently 6.4.6.3.1 in 13R that there would be something in the
> substantiation we could send to the inspector. Or do you think the
> inspector is right, do we need another sprinkler?


> Ron Fletcher
> Aero Automatic
> Phoenix, AZ



> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.1913 / Virus Database: 2411/4958 - Release Date: 04/25/12




-- 
Best regards,
 Charles                            mailto:[email protected]

 Confidentiality Notice: This e-mail message, including any attachments, is
 for the sole purpose of the intended recipients and may contain confidential
 and privileged information.  Any unauthorized review, use, disclosure or
 distribution is prohibited.  If you are not the intended recipient, please 
contact
 the sender by reply e-mail and destroy all copies of the original message.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to