A 1'-0" gap on both sides is pretty large. I would think that the heat would
end up going past any sprinklers in the ceiling (in most cases) and would
need to fill the space above the ceiling before you had a sprinkler
activation. For this delayed activation alone, I would put heads above and
below (and have done so on several occasions). I look at it as a floating
ceiling.

I do agree that the code is a bit unclear on this. I have in the past,
argued both sides of this.

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Tuesday, June 05, 2012 1:18 PM
To: [email protected]
Subject: corridor ceiling

NFPA 2010 is the applicable standard. Drop in ceiling down the corridor on
all four floors of a new construction office building. Non combustible 4'
vertical space above. Ceiling leaves a gap and doesn't connect to the wall
on either side of the corridor. The gap is 1'0 on both sides. Trying to
figure out if sprinklers are required above. I don't see any part of the
standard that clearly addresses this. The closest I can see is the
following:

8.15.1.2.1*<http://codesonline.nfpa.org/a/c.ref/ID00001330400/sec> Concealed
spaces of noncombustible and limited-combustible construction with minimal
combustible loading having no access shall not require sprinkler protection.

8.15.1.2.1.1 The space shall be considered a concealed space even with small
openings such as those used as return air for a plenum.

Do you think that this situation would classify as a concealed space? Do you
think this space requires sprinklers above the ceiling? AHJ statement is to
do it per code. Thanks for any input.

[Description: LOGO_10]
Rod DiBona
Vice President
Rapid Fire Protection
office : (605)348-2342
fax : (605)348-0108
cell : (605)391-3553
www.rapidfireinc.com<http://www.rapidfireinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120605/7265eaa1/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6561 bytes
Desc: image001.jpg
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120605/7265eaa1/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to