Bob / Mike,

Thank you for your thoughts. I certainly can see where it would make sense to 
have to cover above but at the same time I see the reference in 8.15.1.2.1.1 
where small openings don't negate an area from being considered concealed. The 
example given is " such as those used as return air for a plenum"..... Any idea 
how large such an opening would be?

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bob
Sent: Tuesday, June 05, 2012 11:28 AM
To: [email protected]
Subject: RE: corridor ceiling

Mr DiBona,
I hate to say yes, but I believe you will need heads above the ceiling.  In
essence what you have is an obstruction below the sprinklers at the roof
deck.  Because the ceiling is a floating cloud the heat can and most likely
will roll past the edges of the cloud and cause havoc above the ceiling
itself.  This will most likely delay the operating of the lower sprinklers.
The problem that I see is that this is not a concealed space since it is
open on the sides.  

My two cents worth,

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Tuesday, June 05, 2012 11:18 AM
To: [email protected]
Subject: corridor ceiling

NFPA 2010 is the applicable standard. Drop in ceiling down the corridor on
all four floors of a new construction office building. Non combustible 4'
vertical space above. Ceiling leaves a gap and doesn't connect to the wall
on either side of the corridor. The gap is 1'0 on both sides. Trying to
figure out if sprinklers are required above. I don't see any part of the
standard that clearly addresses this. The closest I can see is the
following:

8.15.1.2.1*<http://codesonline.nfpa.org/a/c.ref/ID00001330400/sec> Concealed
spaces of noncombustible and limited-combustible construction with minimal
combustible loading having no access shall not require sprinkler protection.

8.15.1.2.1.1 The space shall be considered a concealed space even with small
openings such as those used as return air for a plenum.

Do you think that this situation would classify as a concealed space? Do you
think this space requires sprinklers above the ceiling? AHJ statement is to
do it per code. Thanks for any input.

[Description: LOGO_10]
Rod DiBona
Vice President
Rapid Fire Protection
office : (605)348-2342
fax : (605)348-0108
cell : (605)391-3553
www.rapidfireinc.com<http://www.rapidfireinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120605/7265eaa1/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6561 bytes
Desc: image001.jpg
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120605/7265eaa1/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2178 / Virus Database: 2433/5048 - Release Date: 06/05/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to