And there's the very simplistic conflict between widely accepted good practices 
for evacuation and the attractive nuisance of a hose station.   We want the 
lift driver to run out of the building ASAP, not grab an appliance they've 
never been trained on and run TOWARDS the fire.    NFPA 25 allows for removal 
of hose during ITM, with the approval of the AHJ.   Boiling existing hose 
stations down to just a valve the could be used by trained personnel in 
response to a fire makes more sense.   Removing them entirely if the responding 
FD has no use for them makes sense.   Installing these valves at the exterior 
fire access points so that responders can connect as they enter the building 
makes sense.   We do have some proactive options available to use as 
installers/inspectors/consultants, but one has to take the bull by the horns 
and reach out to the AHJ to determine the extent of their energies about these 
connections, and also whether they have a preferred course of action.
 
SL

________________________________

From: [email protected] on behalf of Ron Greenman
Sent: Mon 6/11/2012 5:19 PM
To: [email protected]
Subject: Re: 2007 12.2.1 Small hose stations



The problem is who uses these. In an industrial setting with a fire brigade
or at least some guys with a little training in fire fighting and practice
with the hose. I think the problem, or at least as stated to me by FD guys
is you Billy Joe the lift driver shooting water at the top of the flames.
He isn't hurting, probably isn't helping either, but he's in the building
instead of getting out, and when the FD arrives rescue takes precedence
over suppression. The whole scenario gets more dangerous for everyone and
draws in more responders than would otherwise be necessary. Just like
having an entire community sprinklered changes tactical planning I think
eliminating what may be considered an attractive nuisance for the untrained
may have some impact of the FD.

On Mon, Jun 11, 2012 at 4:18 PM, å... .... <[email protected]> wrote:

> Until solid statistical evidence
> is produced, I guess we are left
> will little more than opinions and
> speculation, relegated
> to tossing events and outliers from
> the database and leaving them as
> one-off examples in the rubbish bin
> sample space.
>
> My opinion is America lost some
> serious mojo over its small hose
> issue.
>
>
> *Factory Mutual Data Sheet 8-9*
>
> *§ 3.2 Loss History*
>
> *July 2011 *
>
>
> The use of hoses use was identified in 87% of the incidents that operated
>
> ten or fewer sprinklers and, when hoses were used, they were applied
>
> either before sprinklers operated or before fire control was achieved in
>
> a little more than 50% of the cases. This strong correlation suggests early
>
> application of hose streams has a significant effect on the average number
>
> of sprinklers that operate in rack storage fires (it would follow that this
> is
>
> also true for solid-piled / palletized storage fires), and that provision
> of
>
> small hose stations is a key element in the overall protection scheme.
>
> It is impossible to say how many catastrophic fires may have been
>
> prevented by early intervention using hoses.
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120612/7f38694c/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120611/0f3e727f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120612/53d18338/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to