Pumper outlet, steamer connection, LDH connection.  It's the big connection on 
a 3-way hydrant.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, September 13, 2012 12:03 PM
To: [email protected]
Subject: NFPA 291, 4.8.2

The referenced section and its associated table state that when Pumper
Outlets are used for a flow test, an additional factor is to be applied
in the conversion calculation from pitot PSI to GPM.   Is the term
Pumper Outlets, as used here, referring to a 4" port?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e4aafb89/attachment.html>