In Phoenix the water department will not use the additional modification to the flow test for their "official test", and the fire department requires the adjustment. Mark at Aero
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Thursday, September 13, 2012 10:04 AM To: [email protected] Subject: RE: NFPA 291, 4.8.2 Got that, just not used to taking flow tests from a 4" port and have never had to apply this factor that I can recall. Not too old to pick up a new trick this week ... SL -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Johnson, Duane (NIH/OD/ORS) [C] Sent: Thursday, September 13, 2012 9:58 AM To: [email protected] Subject: RE: NFPA 291, 4.8.2 Realize the coefficients in Table 4.8.2 only apply when performing a test directly off the steamer connection. If you are using a hose monster, the added coefficient is not applicable. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: [email protected] [mailto:[email protected]] Sent: Thursday, September 13, 2012 12:04 PM To: [email protected] Subject: RE: NFPA 291, 4.8.2 Pumper outlet, steamer connection, LDH connection. It's the big connection on a 3-way hydrant. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Thursday, September 13, 2012 12:03 PM To: [email protected] Subject: NFPA 291, 4.8.2 The referenced section and its associated table state that when Pumper Outlets are used for a flow test, an additional factor is to be applied in the conversion calculation from pitot PSI to GPM. Is the term Pumper Outlets, as used here, referring to a 4" port? Steve Leyton PROTECTION DESIGN & CONSULTING 2851 Camino del Rio South, Suite 400 San Diego, CA 92108 ------------------------------------------------------------- Ph: 858.751.2930 - ext. 102 Fax: 858.751.2933 Cell: 619.972.5696 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e4aafb89/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum