Ooops. Hope you had a min. 17% safety factor! The 2.5" outlet is the preferred method...see 4.6.
Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: Steve Leyton [mailto:[email protected]] Sent: Thursday, September 13, 2012 1:04 PM To: [email protected] Subject: RE: NFPA 291, 4.8.2 Got that, just not used to taking flow tests from a 4" port and have never had to apply this factor that I can recall. Not too old to pick up a new trick this week ... SL -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Johnson, Duane (NIH/OD/ORS) [C] Sent: Thursday, September 13, 2012 9:58 AM To: [email protected] Subject: RE: NFPA 291, 4.8.2 Realize the coefficients in Table 4.8.2 only apply when performing a test directly off the steamer connection. If you are using a hose monster, the added coefficient is not applicable. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: [email protected] [mailto:[email protected]] Sent: Thursday, September 13, 2012 12:04 PM To: [email protected] Subject: RE: NFPA 291, 4.8.2 Pumper outlet, steamer connection, LDH connection. It's the big connection on a 3-way hydrant. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Thursday, September 13, 2012 12:03 PM To: [email protected] Subject: NFPA 291, 4.8.2 The referenced section and its associated table state that when Pumper Outlets are used for a flow test, an additional factor is to be applied in the conversion calculation from pitot PSI to GPM. Is the term Pumper Outlets, as used here, referring to a 4" port? Steve Leyton PROTECTION DESIGN & CONSULTING 2851 Camino del Rio South, Suite 400 San Diego, CA 92108 ------------------------------------------------------------- Ph: 858.751.2930 - ext. 102 Fax: 858.751.2933 Cell: 619.972.5696 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e4aafb89/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum