Ooops. Hope you had a min. 17% safety factor!

The 2.5" outlet is the preferred method...see 4.6.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Steve Leyton [mailto:[email protected]] 
Sent: Thursday, September 13, 2012 1:04 PM
To: [email protected]
Subject: RE: NFPA 291, 4.8.2

Got that, just not used to taking flow tests from a 4" port and have never had 
to apply this factor that I can recall.  Not too old to pick up a new trick 
this week ...

SL




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Thursday, September 13, 2012 9:58 AM
To: [email protected]
Subject: RE: NFPA 291, 4.8.2

Realize the coefficients in Table 4.8.2 only apply when performing a test 
directly off the steamer connection. If you are using a hose monster, the added 
coefficient is not applicable. 

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, September 13, 2012 12:04 PM
To: [email protected]
Subject: RE: NFPA 291, 4.8.2

Pumper outlet, steamer connection, LDH connection.  It's the big connection on 
a 3-way hydrant.

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, September 13, 2012 12:03 PM
To: [email protected]
Subject: NFPA 291, 4.8.2

The referenced section and its associated table state that when Pumper
Outlets are used for a flow test, an additional factor is to be applied
in the conversion calculation from pitot PSI to GPM.   Is the term
Pumper Outlets, as used here, referring to a 4" port?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e4aafb89/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to