Got that, just not used to taking flow tests from a 4" port and have never had 
to apply this factor that I can recall.  Not too old to pick up a new trick 
this week ...

SL




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Thursday, September 13, 2012 9:58 AM
To: [email protected]
Subject: RE: NFPA 291, 4.8.2

Realize the coefficients in Table 4.8.2 only apply when performing a test 
directly off the steamer connection. If you are using a hose monster, the added 
coefficient is not applicable. 

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, September 13, 2012 12:04 PM
To: [email protected]
Subject: RE: NFPA 291, 4.8.2

Pumper outlet, steamer connection, LDH connection.  It's the big connection on 
a 3-way hydrant.

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, September 13, 2012 12:03 PM
To: [email protected]
Subject: NFPA 291, 4.8.2

The referenced section and its associated table state that when Pumper
Outlets are used for a flow test, an additional factor is to be applied
in the conversion calculation from pitot PSI to GPM.   Is the term
Pumper Outlets, as used here, referring to a 4" port?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e4aafb89/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to