And so???? Response time difference is only one factor to consider.  Many would 
draw the conclusion 'OMG 100 seconds difference but what about the children'.  
Just because the first sprinkler operates later has NO direct singular 
correlation to the outcome.  This is WHY we use higher temperature heads in 
high heat release heat fires - in order to keep the wet stuff on the red stuff 
(or at least real close factoring in plume dynamics).   So the potential here 
is possibly BETTER fire protection performance because although delayed fewer 
heads operate thus more water where it's needed.  Be careful in drawing any 
conclusions when only doing part of an analysis.

I realize you are not intending your FDS model to be the conclusion of this 
discussion but you, Ron and I are not the only ones reading this forum.  (PS 
anyone know how many subscribers these days?)

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
bcasterl...@fsc-inc.com
Sent: Sunday, September 30, 2012 11:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement

all i got is some numbers:

27' ceiling height, 9" deflector distance, couch on fire in the middle of a 
large, open furniture showroom---

286F, standard response- activation time = 188 seconds 286F, quick response- 
activation time = 172 seconds 212F, standard response- activation time = 97 
seconds 212F, quick response- activation time = 80 seconds

(details available upon request)

regards,
Anyone...?
:)

_______________________________________________