Chris, I see your point about "OMG..."! I was not trying to do anything
elaborate, and the conclusions for the post had been arrived at-- still I
wondered about worst case activation time difference (only). I suppose I
should have kept it to myself. I found the HRR that would be just enough to
activate a 286 SR at 9" below a 27' ceiling in about 180 seconds (my
benchmark). This was about 1 Megawatt, very low, and it produces the
greatest activation time difference (using my benchmark, in my model). If I
used a 2 MW fire, not only would the activation times be less, but so would
the activation time differences (I am going to put numbers to it tonight
after work).
Duane, nice bit about the condensation- it makes sense- the water returns
the heat it soaked up in being vaporized! Another complication for
'sprinkler skipping'. 
I will get off this thread now.  

-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C] [mailto:johnson...@mail.nih.gov] 
Sent: Monday, October 01, 2012 8:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement

Yes, keep the overall picture in mind. RTI is only one aspect. As others
have said, as more sprinklers operate, the discharge density decreases. Why
activate additional sprinklers and decrease the density if it is not
necessary? 

One more piece of info for high heat release rate fires and the use of high
temp sprinklers. The water discharged from the sprinklers can be returned to
the ceiling as steam. The steam can condense on sprinklers outside the fire
area and activate the sprinklers (see commentary for 8.3.2.4). Once again,
it can be detrimental to the system design to activate sprinklers outside
the fire area. This is one reason why intermediate and high temp sprinklers
are used in storage apps.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Cahill, Christopher [mailto:ccah...@burnsmcd.com] 
Sent: Monday, October 01, 2012 8:13 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement

And so???? Response time difference is only one factor to consider.  Many
would draw the conclusion 'OMG 100 seconds difference but what about the
children'.  Just because the first sprinkler operates later has NO direct
singular correlation to the outcome.  This is WHY we use higher temperature
heads in high heat release heat fires - in order to keep the wet stuff on
the red stuff (or at least real close factoring in plume dynamics).   So the
potential here is possibly BETTER fire protection performance because
although delayed fewer heads operate thus more water where it's needed.  Be
careful in drawing any conclusions when only doing part of an analysis.

I realize you are not intending your FDS model to be the conclusion of this
discussion but you, Ron and I are not the only ones reading this forum.  (PS
anyone know how many subscribers these days?)

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
bcasterl...@fsc-inc.com
Sent: Sunday, September 30, 2012 11:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement

all i got is some numbers:

27' ceiling height, 9" deflector distance, couch on fire in the middle of a
large, open furniture showroom---

286F, standard response- activation time = 188 seconds 286F, quick response-
activation time = 172 seconds 212F, standard response- activation time = 97
seconds 212F, quick response- activation time = 80 seconds

(details available upon request)

regards,
Anyone...?
:)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to