Yes, keep the overall picture in mind. RTI is only one aspect. As others have 
said, as more sprinklers operate, the discharge density decreases. Why activate 
additional sprinklers and decrease the density if it is not necessary? 

One more piece of info for high heat release rate fires and the use of high 
temp sprinklers. The water discharged from the sprinklers can be returned to 
the ceiling as steam. The steam can condense on sprinklers outside the fire 
area and activate the sprinklers (see commentary for 8.3.2.4). Once again, it 
can be detrimental to the system design to activate sprinklers outside the fire 
area. This is one reason why intermediate and high temp sprinklers are used in 
storage apps.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Cahill, Christopher [mailto:ccah...@burnsmcd.com] 
Sent: Monday, October 01, 2012 8:13 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement

And so???? Response time difference is only one factor to consider.  Many would 
draw the conclusion 'OMG 100 seconds difference but what about the children'.  
Just because the first sprinkler operates later has NO direct singular 
correlation to the outcome.  This is WHY we use higher temperature heads in 
high heat release heat fires - in order to keep the wet stuff on the red stuff 
(or at least real close factoring in plume dynamics).   So the potential here 
is possibly BETTER fire protection performance because although delayed fewer 
heads operate thus more water where it's needed.  Be careful in drawing any 
conclusions when only doing part of an analysis.

I realize you are not intending your FDS model to be the conclusion of this 
discussion but you, Ron and I are not the only ones reading this forum.  (PS 
anyone know how many subscribers these days?)

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
bcasterl...@fsc-inc.com
Sent: Sunday, September 30, 2012 11:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement

all i got is some numbers:

27' ceiling height, 9" deflector distance, couch on fire in the middle of a 
large, open furniture showroom---

286F, standard response- activation time = 188 seconds 286F, quick response- 
activation time = 172 seconds 212F, standard response- activation time = 97 
seconds 212F, quick response- activation time = 80 seconds

(details available upon request)

regards,
Anyone...?
:)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to