It is also not going to trip or be severely delayed if there is a water column 
occurrence holding the clapper shut.  

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Wednesday, October 24, 2012 11:06 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: trip time per nfpa 25

I don't believe their is any reference to "how long is too long" except in
13 (pre 2010) where a system of between 500 & 750 gallons is required to have a 
QOD if the water delivery time to the inspectors test exceeds 60 seconds. I 
think there is a presumption that a system of less than 500 gallons will trip 
in a "timely" manner, that over 750 gallons won't without a QOD, and that in 
between one is questionable. From there the one minute trip time came to be the 
conventional standard, although the book only referred to water delivery time 
after the trip occurred. In the 2010 edition times are specified. See section 
7.2.3.6 Dry Pipe System Water Delivery. Although entitled as "water delivery 
time" it tells you that the delivery time countdown starts at normal air 
pressure which suggests pre-trip, tto the actual trip, and finishing with water 
at the test port.

On Wed, Oct 24, 2012 at 10:27 AM, Gregg Key <gr...@keyfps.com> wrote:

> Our inspector ask an interesting question today. How long is too long 
> of a time for a dry valve to trip before it is considered a 
> deficiency? 25 does not specify but 15 min seams too long. Don't have 
> the previous report to compare it to.
>
> C.Gregg Key, SET
> Key Fire Protection Services,Inc
> Project Manager
> (O) 706-790-3473
> (C) 706-220-8821
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121024/57fe47b6/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to