Very good feedback. This system was installed in 2006 and is a Victaulic
dpv. We have none of the original acceptance test paperwork but would make
an assumption that it would have passed then. It appears to be a small
system. Mike ,you are right about the by-pass line as it appears that there
is not one installed. Air Compressor is in a hidden crawl space below the
floor. My thought was that something has restricted the air release in the
inspectors test but have not taken it apart. Thanks for everyones help 

C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Cabral
Sent: Thursday, October 25, 2012 10:40 AM
To: sprinklerforum@firesprinkler.org
Cc: sprinklerforum@firesprinkler.org
Subject: Re: trip time per nfpa 25

I would check to make sure that the air supply to the DPV is working as it
should. The time to trip should never be that long. Is the by-pass open?
Sounds like the make-up air is supplying to much air. The make up air needs
to be restricted. The supply line to the Inspectors Test can be larger than
1" it can't be less than 1" however the standard does no say it can't be
larger than 1". 

Sent from my iPhone

On Oct 24, 2012, at 1:13 PM, Todd Letterman <tletter...@haifire.com> wrote:

> It is also not going to trip or be severely delayed if there is a water
column occurrence holding the clapper shut.  
> 
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org 
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron 
> Greenman
> Sent: Wednesday, October 24, 2012 11:06 AM
> To: sprinklerforum@firesprinkler.org
> Subject: Re: trip time per nfpa 25
> 
> I don't believe their is any reference to "how long is too long" 
> except in
> 13 (pre 2010) where a system of between 500 & 750 gallons is required to
have a QOD if the water delivery time to the inspectors test exceeds 60
seconds. I think there is a presumption that a system of less than 500
gallons will trip in a "timely" manner, that over 750 gallons won't without
a QOD, and that in between one is questionable. From there the one minute
trip time came to be the conventional standard, although the book only
referred to water delivery time after the trip occurred. In the 2010 edition
times are specified. See section 7.2.3.6 Dry Pipe System Water Delivery.
Although entitled as "water delivery time" it tells you that the delivery
time countdown starts at normal air pressure which suggests pre-trip, tto
the actual trip, and finishing with water at the test port.
> 
> On Wed, Oct 24, 2012 at 10:27 AM, Gregg Key <gr...@keyfps.com> wrote:
> 
>> Our inspector ask an interesting question today. How long is too long 
>> of a time for a dry valve to trip before it is considered a 
>> deficiency? 25 does not specify but 15 min seams too long. Don't have 
>> the previous report to compare it to.
>> 
>> C.Gregg Key, SET
>> Key Fire Protection Services,Inc
>> Project Manager
>> (O) 706-790-3473
>> (C) 706-220-8821
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.org
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> rgreen...@bates.ctc.edu
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis 
> Bacon, essayist, philosopher, and statesman (1561-1626)
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20121024/57fe47b6/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to