Okay, I stand corrected...my previous post below states that I would require sprinklers in these closets on the breezeways unless 13R excludes them.
2007 editon, pargargph 6.9.7 - allowed sprinklers to be omitted from closets on the exterior balconies which did not open into the dwelling units. 2010 edition, paragraph 6.6.7 - allowed sprinklers to be omitted from the closets on the exterior balconies...AND exterior breezeways/corridors which did not open into the dwelling units. The NFPA committee appears to have made a change specifically to tell me... "Hey stupid, we're putting this omission in the standard just because you keep requiring sprinklers in these closets on the breezeways". Please also read the 2013 edition. - Paragraph 6.6.5 still allows sprinkler omission from the balconies, but paragraph 6.6.5.1 requires sprinklers on the balconies if Type V (wood frame) construction. No mention is made of requiring sprinklers in breezeways of Type V construction. - Annex paragraph A.6.6.5 now shows figures of the types of "corridors" or breezeways which could be allowed without sprinklers. The committee appears to have added these to correct me here as well as I previously allowed only straight-thru breezeways without sprinklers. - Paragraph 6.6.7 still allows sprinklers to be omitted from the exterior closets....so you have to sprinkler the balconies of Type V construction, but you can omit the sprinklers from the closets on these balconies. I agree with Ron Greenman's statement, "Personally I'm not a fan of 13R at all"...as I feel that sprinklers should be installed throughtout the dwelings...including the dog house...but these residential standards were written to mitigate the costs of the sprinkler systems and still provide a level of life safety. This has allowed for a cost-effective means for installing more sprinkler systems in residential buildings...which is a good thing. I may not agree with the changes, but I will try to follow to the best of my abillity to meet the requirements of the standards with the guidance provided in the annex and the handbooks. Respectfully, rick matsuda city of dallas -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matsuda, Richard Sent: Wednesday, February 13, 2013 9:04 AM To: [email protected] Subject: RE: Exterior closets....again but different Steve, Are you addressing me in this email?...or some other Rick? If you're asking my opinion, then I'll agree with what was stated by the local AHJ in the last sentence of the original posting from Rod. "He says show me in 13R where you can exclude....." rick matsuda city of dallas, building insp dept. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Wednesday, February 13, 2013 10:25 AM To: [email protected] Subject: RE: Exterior closets....again but different I suppose my opinion goes to the idea (shared by most AHJ's, right Rick?) that there is not necessarily an absolute control over what happens in those closets after the fact. Without seeing the plans, or knowing the size of the compartments, one could say that HOA or building management might use them for storage in the future. Besides the section you just cited, 2013 edition, new section 6.6.8 states, "All situations regarding sprinkler location and position that are not directly discussed in FPA 13R shall be in accordance with NFPA 13." Admittedly, you could read the breezeway closet exception the other way as it doesn't specifically say that the excepted closets would have to be associated with a dwelling unit (i.e. of a residential-type use). It can also be said that the revised A.1.1 in the new standard also confuses the issue a bit. To clarify what I said last night, without digging into the minutiae of interpretation, I agree with the AHJ that if there's any doubt about the intent of the standard, just put in sprinklers. Steve -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Rod DiBona Sent: Wednesday, February 13, 2013 8:19 AM To: [email protected] Subject: RE: Exterior closets....again but different Steve, I think the following is where I went wrong with the previous post. 13R - 6.9.1 Sprinklers shall be installed in all areas except where omission is permitted by 6.9.2 - 6.9.7. Thanks, Rod -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Rod DiBona Sent: Wednesday, February 13, 2013 8:34 AM To: [email protected] Cc: Brent Zimiga Subject: RE: Exterior closets....again but different Steve, Thank you for your response. I do agree that the contested closets are outside the dwelling unit. I am looking but haven't found where 13R says that areas outside the dwelling unit shall be PROTECTED by 13. I see 6.8.2.1 that says "For areas outside the dwelling unit, the design discharge and design area criteria shall comply with NFPA 13"....No mention of coverage?... For example, we don't sprinkler concealed combustible and attics in 13R which are outside the dwelling unit. So this is the heart of the issue does chapter 8 of 13 apply? Is so where does 13R state that it does apply for protection of areas? If it does apply, then the 13R exemptions for other areas outside the dwelling unit trump 13 requirements? Not trying to be difficult and this is not a big add to the project but truly want to come to an understanding on this one. Wonder why the closets on the decks would be exempted but not a breezeway? Egress? Thanks! Rod at Rapid -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Tuesday, February 12, 2013 10:52 PM To: [email protected] Subject: RE: Exterior closets....again but different I agree with the AHJ. Exception to closets on exterior balconies presumes they are within (or directly communicating with) dwelling unit. If you agree that the contested closets are outside of the dwelling unit, where is the exception in 13 that would not require sprinklers in these compartments? Methinks you're trying to split hairs with the "design criteria" intent argument - what do you mean by that, exactly? If hydraulics, then the answer is yes, but 13R also states that areas outside the dwelling unit shall be protected per 13, so I think that Chapter 8 of 13 applies, period. The foregoing is my opinion only, and does not necessarily represent the opinion or intent of the Technical Committee on Residential Sprinkler Systems. Steve L. -----Original Message----- From: [email protected] on behalf of Rod DiBona Sent: Tue 2/12/2013 4:25 PM To: [email protected] Subject: Exterior closets....again but different NFPA 13R 2007- New apartment building with a breezeway on the bottom level that is enclosed and protected with dry sidewalls. 2 closets (one plumbing and the other electrical data) in that breezeway that only open to the breezeway. No fuel fired equipment. No heating or air conditioning equipment. Had it in my mind that these closets would not have to be sprinklered. Fire marshal is disagreeing. After review I am not so sure. Seems like the intent is to not require protection but by the letter I can't quite get there. Am I missing something? 2007 NFPA 13R 6.9.6 - "Sprinklers shall not be required in............(last sentence) ... "and other concealed spaces that are not intended for living purposes or storage and do not contain fuel fired equipment." - He pointed out that a closet is not a concealed space...... Ok then..... 2007 NFPA 13R 6.9.7 " Sprinklers shall not be required in closets on exterior balconies, regardless of size, as long as there are no doors or unprotected penetrations from the closet directly into the dwelling unit. - His point is that these closets are not on exterior balconies.... He says that it is outside the dwelling unit and therefore protected by NFPA 13. My comment is that I believe 2007 NFPA 13R only requires the "design criteria" of 13 to be followed for areas outside the dwelling unit. Clarified in section A.6.8.2. He says show me in 13R where you can exclude..... Thoughts? Rod DiBona Vice President Rapid Fire Protection office : (605)348-2342 fax : (605)348-0108 cell : (605)391-3553 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum