Rick,

I think that the desire require of sprinklering of hotels, dorms,
apartments, etc., in the building code was the impetuous for developing the
"life-safety" system as represented by 13R & 13D. I can remember when
seattle was happy with corridor/egress only protection if that would get
some level of protection installed. Although we still have a long row only
partially hoed regarding SFDs the stuff covered by 13R is pretty much a
given, at least in the higher density areas (notwithstanding San Diego,
Chicago, and NYC), at it's time to retire it into 13. There can still be
some special exceptions (I know we can't call them that anymore but....)
for these four-story guys. Up here we're seeing five-story sticks builds on
top of a couple of stories of concrete, and with the dormer  roof floor not
being called a story because it's a roofline, and so sprinklering the
sticks to 13R. I don't think this is the intent (sarcasticon here) and such
abuse shouldn't be allowed.

On Fri, Feb 15, 2013 at 8:38 AM, Matsuda, Richard <
[email protected]> wrote:

> Okay, I stand corrected...my previous post below states that I would
> require sprinklers in these closets on the breezeways unless 13R
> excludes them.
>
> 2007 editon, pargargph 6.9.7 - allowed sprinklers to be omitted from
> closets on the exterior balconies which did not open into the dwelling
> units.
>
> 2010 edition, paragraph 6.6.7 - allowed sprinklers to be omitted from
> the closets on the exterior balconies...AND exterior
> breezeways/corridors which did not open into the dwelling units.
>
> The NFPA committee appears to have made a change specifically to tell
> me... "Hey stupid, we're putting this omission in the standard just
> because you keep requiring sprinklers in these closets on the
> breezeways".
>
> Please also read the 2013 edition.
> - Paragraph 6.6.5 still allows sprinkler omission from the balconies,
> but paragraph 6.6.5.1 requires sprinklers on the balconies if Type V
> (wood frame) construction. No mention is made of requiring sprinklers in
> breezeways of Type V construction.
> - Annex paragraph A.6.6.5 now shows figures of the types of "corridors"
> or breezeways which could be allowed without sprinklers. The committee
> appears to have added these to correct me here as well as I previously
> allowed only straight-thru breezeways without sprinklers.
> - Paragraph 6.6.7 still allows sprinklers to be omitted from the
> exterior closets....so you have to sprinkler the balconies of Type V
> construction, but you can omit the sprinklers from the closets on these
> balconies.
>
> I agree with Ron Greenman's statement, "Personally I'm not a fan of 13R
> at all"...as I feel that sprinklers should be installed throughtout the
> dwelings...including the dog house...but these residential standards
> were written to mitigate the costs of the sprinkler systems and still
> provide a level of life safety. This has allowed for a cost-effective
> means for installing more sprinkler systems in residential
> buildings...which is a good thing.
>
> I may not agree with the changes, but I will try to follow to the best
> of my abillity to meet the requirements of the standards with the
> guidance provided in the annex  and the handbooks.
> Respectfully,
> rick matsuda
> city of dallas
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Matsuda,
> Richard
> Sent: Wednesday, February 13, 2013 9:04 AM
> To: [email protected]
> Subject: RE: Exterior closets....again but different
>
> Steve,
> Are you addressing me in this email?...or some other Rick?
> If you're asking my opinion, then I'll agree with what was stated by the
> local AHJ in the last sentence of the original posting from Rod.
> "He says show me in 13R where you can exclude....."
>
> rick matsuda
> city of dallas, building insp dept.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Wednesday, February 13, 2013 10:25 AM
> To: [email protected]
> Subject: RE: Exterior closets....again but different
>
> I suppose my opinion goes to the idea (shared by most AHJ's, right
> Rick?) that there is not necessarily an absolute control over what
> happens in those closets after the fact.  Without seeing the plans, or
> knowing the size of the compartments, one could say that HOA or building
> management might use them for storage in the future.   Besides the
> section you just cited, 2013 edition, new section 6.6.8 states, "All
> situations regarding sprinkler location and position that are not
> directly discussed in FPA 13R shall be in accordance with NFPA 13."
>
> Admittedly, you could read the breezeway closet exception the other way
> as it doesn't specifically say that the excepted closets would have to
> be associated with a dwelling unit (i.e. of a residential-type use).  It
> can also be said that the revised A.1.1 in the new standard also
> confuses the issue a bit.   To clarify what I said last night, without
> digging into the minutiae of interpretation, I agree with the AHJ that
> if there's any doubt about the intent of the standard, just put in
> sprinklers.
>
> Steve
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Rod
> DiBona
> Sent: Wednesday, February 13, 2013 8:19 AM
> To: [email protected]
> Subject: RE: Exterior closets....again but different
>
> Steve,
>
> I think the following is where I went wrong with the previous post.
>
> 13R - 6.9.1 Sprinklers shall be installed in all areas except where
> omission is permitted by 6.9.2 - 6.9.7.
> Thanks,
>
> Rod
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Rod
> DiBona
> Sent: Wednesday, February 13, 2013 8:34 AM
> To: [email protected]
> Cc: Brent Zimiga
> Subject: RE: Exterior closets....again but different
>
> Steve,
>
> Thank you for your response. I do agree that the contested closets are
> outside the dwelling unit. I am looking but haven't found where 13R says
> that areas outside the dwelling unit shall be PROTECTED by 13. I see
> 6.8.2.1 that says "For areas outside the dwelling unit, the design
> discharge and design area criteria shall comply with NFPA 13"....No
> mention of coverage?... For example, we don't sprinkler concealed
> combustible and attics in 13R which are outside the dwelling unit. So
> this is the heart of the issue does chapter 8 of 13 apply? Is so where
> does 13R state that it does apply for protection of areas? If it does
> apply, then the 13R exemptions for other areas outside the dwelling unit
> trump 13 requirements? Not trying to be difficult and this is not a big
> add to the project but truly want to come to an understanding on this
> one. Wonder why the closets on the decks would be exempted but not a
> breezeway? Egress? Thanks!
>
> Rod at Rapid
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Tuesday, February 12, 2013 10:52 PM
> To: [email protected]
> Subject: RE: Exterior closets....again but different
>
> I agree with the AHJ.   Exception to closets on exterior balconies
> presumes they are within (or directly communicating with) dwelling unit.
> If you agree that the contested closets are outside of the dwelling
> unit, where is the exception in 13 that would not require sprinklers in
> these compartments?  Methinks you're trying to split hairs with the
> "design criteria" intent argument - what do you mean by that, exactly?
> If hydraulics, then the answer is yes, but 13R also states that areas
> outside the dwelling unit shall be protected per 13, so I think that
> Chapter 8 of 13 applies, period.
>
> The foregoing is my opinion only, and does not necessarily represent the
> opinion or intent of the Technical Committee on Residential Sprinkler
> Systems.
>
> Steve L.
>
>
> -----Original Message-----
> From: [email protected] on behalf of Rod DiBona
> Sent: Tue 2/12/2013 4:25 PM
> To: [email protected]
> Subject: Exterior closets....again but different
>
> NFPA 13R 2007- New apartment building with a breezeway on the bottom
> level that is enclosed and protected with dry sidewalls. 2 closets (one
> plumbing and the other electrical data) in that breezeway that only open
> to the breezeway. No fuel fired equipment. No heating or air
> conditioning equipment. Had it in my mind that these closets would not
> have to be sprinklered. Fire marshal is disagreeing. After review I am
> not so sure. Seems like the intent is to not require protection but by
> the letter I can't quite get there. Am I missing something?
>
> 2007 NFPA 13R 6.9.6 - "Sprinklers shall not be required
> in............(last sentence) ... "and other concealed spaces that are
> not intended for living purposes or storage and do not contain fuel
> fired equipment." -   He pointed out that a closet is not a concealed
> space...... Ok then.....
>
> 2007 NFPA 13R 6.9.7 " Sprinklers shall not be required in closets on
> exterior balconies, regardless of size, as long as there are no doors or
> unprotected penetrations from the closet directly into the dwelling
> unit. - His point is that these closets are not on exterior
> balconies....
>
> He says that it is outside the dwelling unit and therefore protected by
> NFPA 13. My comment is that I believe 2007 NFPA 13R only requires the
> "design criteria" of 13 to be followed for areas outside the dwelling
> unit.  Clarified in section A.6.8.2.
>
> He says show me in 13R where you can exclude.....
>
> Thoughts?
>
> Rod DiBona
> Vice President
> Rapid Fire Protection
> office : (605)348-2342
> fax : (605)348-0108
> cell : (605)391-3553
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130215/af5412d9/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to