Hello Jay,

I had the same thing happening here on a large gridded system that was 
improperly itched. Found lots of trapped air was causing this.

Wednesday, February 20, 2013, 6:55:16 AM, you wrote:

> We have a wet system that is having problems with the flow switch. 
> The flow switch would send a signal and then stop and then send
> another signal.  This would be happening intermittently.  We figured
> the flow switch diaphram was bad and then replaced the flow switch
> with the same results.  The main drain test is 60 psi with 50 psi
> residual.  The inspector's test was a globe valve that would flow
> water intermittantly; so we changed it to a ball valve.  It flows
> water continuously now with the same problem with the flow switch. 
> We checked the vane on the flow switch and the pipe is clean, so
> it's not hanging up at the riser.  Any suggestions?


>  
> Jay Stough
> Tilley fire Equipment Co.