JD A.5.2.1.1.2(5) mentions sprinklers loaded with DUST. I understand this is a powder coating operation and not paint. Maybe the Fire Inspector believes the powder residue is removable in the same manner as the "dust" mentioned above; of course this is only possible if it didn't adhere. If it can be cleaned, as described in 25, then ok. If it cannot then I think changing them is in order and after they are changed overspray protection per NFPA 13 - 2013 6.2.6.4 needs to be applied to the sprinklers and maintained.
Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell www.keyfireprotection.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of JD Gamble Sent: Wednesday, April 24, 2013 6:02 PM To: [email protected] Subject: Cleaning Sprinklers Anyone out there want to address the 'cleaning' of sprinklers as included in NFPA 25, 2011 Ed. A.5.2.1.1.2(5) - In lieu of replacing sprinklers that are loaded with dust, it is permitted to clean sprinklers with compressed air or by a vacuum provided that the equipment does not touch the sprinkler. I have a situation where this is being interpreted to mean that sprinklers covered with residue from a powder coating operation are to be cleaned by order of the Fire Inspector. Also, who can we contact with the NFPA 25 that may have already or will address the intent of the above standard. Thanks, JD Gamble Life Safety Solutions of Sheridan 307-763-3361 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2013.0.3272 / Virus Database: 3162/6270 - Release Date: 04/24/13 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org