For the 2nd part of your question you can request a technical interpretation of 
that section of the standard as indicated below. I copied this from the NPFA 
web site.

Technical questions
      
We've created a more efficient way for members and Public Sector Officials/AHJs 
to submit questions about codes and standards to NFPA staff. Our Technical 
Questions Service provides a convenient way to receive timely and consistent 
technical assistance when you need to know more about NFPA codes and standards 
relevant to your work. Responses are provided by NFPA staff on an informal 
basis.

To submit a question by phone:

*Call +1 800 344-3555, option 3, between the hours of 9:00am-5:00pm (EST) 
Monday through Friday. Please have your NFPA membership number on-hand.
To submit a question online:

*Visit the relevant document information page by selecting your document from 
the complete list of NFPA codes and standards. You may also go directly to a 
document information page by typing "www.nfpa.org/document#" (ie. 
www.nfpa.org/70) in your browser address bar.

*Select the "Technical Questions" tab on the document information page.
Not an NFPA member? Join NFPA today to get access to technical support and 
information to help you make the right choices in your on-the-job decisions.

Important Notice: NFPA's Technical Questions Service is meant to provide 
information on and assistance in accessing and understanding NFPA codes and 
standards. Interpretations and opinions contained in responses provided in 
fulfilling this service do not constitute Formal Interpretations issued 
pursuant to NFPA Regulations. Any opinion expressed, therefore, is the personal 
opinion of the responder and does not necessarily represent the official 
position of the NFPA or its Technical Committees. In addition, responses 
provided are not intended, nor should they be relied upon, to provide 
professional consultation or services.


Regards,
 
mike
 
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of JD Gamble
Sent: Wednesday, April 24, 2013 6:02 PM
To: [email protected]
Subject: Cleaning Sprinklers

Anyone out there want to address the 'cleaning' of sprinklers as included in 

NFPA 25, 2011 Ed.
A.5.2.1.1.2(5) - In lieu of replacing sprinklers that are loaded with dust, it 
is permitted to clean sprinklers with compressed air or by a vacuum provided 
that the equipment does not touch the sprinkler.

I have a situation where this is being interpreted to mean that sprinklers 
covered with residue from a powder coating operation are to be cleaned by order 
of the Fire Inspector.

Also,  who can we contact with the NFPA 25 that may have already or will 
address the intent of the above standard.

Thanks,

JD Gamble
Life Safety Solutions of Sheridan

307-763-3361
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to