Yes that is the correct way to control a separate zone. With a pressure 
reducing valve. It is stated in nfpa 20

Thank you,
Sean Roberts

4456 Campbell RD, Houston, TX 77041
713-896-9941
Fax 713-896-9945
Cell 713-206-8837
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Joe Powell
Sent: Monday, June 03, 2013 12:01 PM
To: [email protected]
Subject: Fire Pump - Pressue Relief Valve

Does the 2010 NFPA 20 allow PRV's to be used to limit pressure on a fire pump 
system?  

The insurance inspector wants the existing pressure reducing valve to be 
replaced with a pressure relief valve. The pressure reducing valve is 
downstream of the fire pump and  limits pressure on a supply to an older part 
of the facility.