Yes that is the correct way to control a separate zone. With a pressure reducing valve. It is stated in nfpa 20
Thank you, Sean Roberts 4456 Campbell RD, Houston, TX 77041 713-896-9941 Fax 713-896-9945 Cell 713-206-8837 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Joe Powell Sent: Monday, June 03, 2013 12:01 PM To: [email protected] Subject: Fire Pump - Pressue Relief Valve Does the 2010 NFPA 20 allow PRV's to be used to limit pressure on a fire pump system? The insurance inspector wants the existing pressure reducing valve to be replaced with a pressure relief valve. The pressure reducing valve is downstream of the fire pump and limits pressure on a supply to an older part of the facility. Joe C. Powell Pruett Ford & Associates, Inc. Consulting Engineers 1201 Broad Street, Suite 3A Augusta, GA 30901 Ph: 706-722-3959 Fax: 706-724-5127 Email: [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org