A.4.7.7   A pressure relief valve is not an acceptable method of reducing 
system pressure under normal operating conditions. Prior to the 2003 edition, 
NFPA 20 did not strictly prohibit the use of pressure relief valves for 
management of excessive pressure at churn or low water flow conditions and only 
recognized it as a poor design practice as part of the 1999 edition. Existing 
installations designed under previous editions of NFPA 20 and containing 
pressure relief valves designed for such purposes might still be in service.
 

4.7.7.1   The net pump shutoff (churn) pressure plus the maximum static suction 
pressure, adjusted for elevation, shall not exceed the pressure for which the 
system components are rated.
 
When selecting the fire pump, the maximum pump discharge pressure should not 
subject any system component to a pressure that exceeds the component pressure 
rating. The maximum discharge pressure normally occurs at zero flow (churn) and 
is calculated by adding the suction pressure to the net pump pressure. The 
maximum reasonably anticipated suction pressure should be used for this 
calculation. All listed fire protection components have a pressure rating of 
175 psi (12.1 bar) or higher. If the system components have been properly 
selected, some fire protection systems may be rated for 300 psi (20.7 bar). 
Pressures in excess of the component rating can damage system components. The 
maximum pressure permitted in a standpipe system per NFPA 14, Standard for the 
Installation of Standpipe and Hose Systems, currently is 350 psi (24.1 bar), 
although NFPA 14 does not restrict the pressure in express risers in standpipe 
systems. See Exhibit II.4.2 for a check valve rated for 300 psi (20.7 bar).
 
















View Large 






EXHIBIT II.4.2. 


Print 



Check Valve Listed for 300 psi (20.7 bar). (Courtesy of Aon Fire Protection 
Engineering)
 







4.7.7.2*   Pressure relief valves and pressure regulating devices in the fire 
pump installation shall not be used as a means to meet the requirements of 
4.7.7.1.
 
The use of pressure relief valves is limited in this standard to the following 
situations:
 

■
Diesel engine drivers where pressures developed may exceed the pressure rating 
of system components if an overspeed condition occurs

 
■
Variable speed drivers where pressures developed may exceed the pressure rating 
of system components if a failure causes the driver to revert to rated speed

 
A pump should never be deliberately oversized so that a pressure reducing valve 
is needed. Pressure reducing valves and pressure relief valves are maintenance 
intensive and should be incorporated into the design of a fire pump system only 
when necessary and allowed by this standard. Pressure reducing valves are not 
permitted to be installed in the fire pump system piping. Where pump discharge 
pressures exceed 175 psi (12.1 bar), flanged cast-iron valves and fittings 
between the fire pump discharge flange and the discharge isolation valve must 
be extra heavy pattern. It is not the intent of Section 4.7.7.2 to limit the 
use of pressure reducing valves or pressure regulating valves downstream of the 
discharge isolation valve. The use of pressure regulating valves downstream of 
the discharge isolation valve is covered in other standards. In many cases, 
high-pressure output is needed to meet the design requirements of systems 
installed in high-rise buildings and in standpipe systems in particular.
 


A.4.7.7.2   It is not the intent of this subsection to restrict the use of 
pressure reducing valves downstream of the discharge isolation valve for the 
purpose of meeting the requirements of 4.7.7.

Thank you,
Sean Roberts

4456 Campbell RD, Houston, TX 77041
713-896-9941
Fax 713-896-9945
Cell 713-206-8837
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Monday, June 03, 2013 12:05 PM
To: [email protected]
Subject: RE: Fire Pump - Pressue Relief Valve

I believe the correct answer is NFPA 20 does not allow this, but NFPA 20 only 
governs the fire pump itself, so anything downstream of the discharge is 
governed by 13/14/etc and the PRV would be the correct, while maybe not 
preferable, solution.
 
 
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com <http://www.bmwc.com/> 
 

________________________________

From: [email protected] on behalf of Joe Powell
Sent: Mon 6/3/2013 1:00 PM
To: [email protected]
Subject: Fire Pump - Pressue Relief Valve



Does the 2010 NFPA 20 allow PRV's to be used to limit pressure on a fire pump 
system? 

The insurance inspector wants the existing pressure reducing valve to be 
replaced with a pressure relief valve. The pressure reducing valve is 
downstream of the fire pump and  limits pressure on a supply to an older part 
of the facility.

Joe C. Powell
Pruett Ford & Associates, Inc.
Consulting Engineers
1201 Broad Street, Suite 3A
Augusta, GA 30901
Ph:     706-722-3959
Fax:    706-724-5127
Email: [email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org