I believe the correct answer is NFPA 20 does not allow this, but NFPA 20 only 
governs the fire pump itself, so anything downstream of the discharge is 
governed by 13/14/etc and the PRV would be the correct, while maybe not 
preferable, solution.
 
 
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com <http://www.bmwc.com/> 
 

________________________________

From: [email protected] on behalf of Joe Powell
Sent: Mon 6/3/2013 1:00 PM
To: [email protected]
Subject: Fire Pump - Pressue Relief Valve



Does the 2010 NFPA 20 allow PRV's to be used to limit pressure on a fire
pump system? 

The insurance inspector wants the existing pressure reducing valve to be
replaced with a pressure relief valve. The pressure reducing valve is
downstream of the fire pump and  limits pressure on a supply to an older
part of the facility.