exactly.  NFPA 14 gives a lot of detail on how to accomplish this set-up.  
Using a relief valve is a big no-no.  Dumping a bunch of water every time you 
do a churn test (weekly for diesel and monthly for electric) is a bad thing 
that is not allowed by NFPA 20.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jun 3, 2013, at 10:04 AM, "Morey, Mike" <[email protected]> wrote:

> I believe the correct answer is NFPA 20 does not allow this, but NFPA 20 only 
> governs the fire pump itself, so anything downstream of the discharge is 
> governed by 13/14/etc and the PRV would be the correct, while maybe not 
> preferable, solution.
> 
> 
> 