Sorry for the late chime in - I'm (theoretically) on vacation and don't have 
NFPA 20 with me.  

As already stated, the 20 yields to other standards that may incorporate a fire 
pump into an approved water supply - 13, 14, 24, etc.   Where 20 ends isn't 
defined, but the discharge control valve is as good a place as any.  14 allows 
segregating a building into zones using pressure reducing valves, but as Roland 
said there is a complex redundancy and potentially higher and lower flow rates 
that must be addressed and such zones could be comprised of 4 reducing valves.

But 20 speaks to correct sizing, albeit in the annex.  I want to say it's 
A.4.7.4, but as I said I don't have the book with so it may be a different 
section.  In any case, it recommends that a pump be sized so that demand falls 
between 90-140% of rating.  To arbitrarily oversize a pump (as specifying 
engineers are sometimes wont to do) and then slap a reducing (or worse, relief) 
valve into the discharge main is a bad practice.  So if you have a pump that's 
oversized for the application, that arguably should be addressed in a more 
meaningful remedial way.   

You say that an insurance rep wants to limit pressure to an "older" part of the 
facility - why?  What's the pressure?   What's the underlying intent and is the 
pump correctly sized for the greater demand(s) of the newer part of the 
protected premises?   Under selected circumstances, a listed reducing valve is 
a good solution, so long as it's installed per listing, applicable standard (13 
and/or 14) and ...  this is the tricky part ... REGULARLY INSPECTED AND TESTED 
PER 25.

Steve L.
Inafoodcoma
New Orleans, LA


-----Original Message-----
From: [email protected] on behalf of Joe Powell
Sent: Mon 6/3/2013 10:00 AM
To: [email protected]
Subject: Fire Pump - Pressue Relief Valve
 
Does the 2010 NFPA 20 allow PRV's to be used to limit pressure on a fire
pump system?  

The insurance inspector wants the existing pressure reducing valve to be
replaced with a pressure relief valve. The pressure reducing valve is
downstream of the fire pump and  limits pressure on a supply to an older
part of the facility.

Joe C. Powell 
Pruett Ford & Associates, Inc. 
Consulting Engineers 
1201 Broad Street, Suite 3A 
Augusta, GA 30901 
Ph:     706-722-3959 
Fax:    706-724-5127 
Email: [email protected] 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to