E M B A R A S S E D!
And so goes my day. I -THOUGHT- I moused 13 and not 13D. I had 'em
all opened.
Thanks for the looksee forum. I'm gonna go back and put the heads back in
in the garage!
At 02:05 PM 6/20/2013, you wrote:
Looks like you're looking in 13D and not 13 w/ that code section.
According to NFPA 13 garages are an ordinary hazard group I occupancy.
On Thu, Jun 20, 2013 at 10:28 AM, Vince Sabolik <[email protected]> wrote:
> Good afternoon, forum --
>
> Using 13R applying to a 3 story condo....
>
> 7.3 Design Criteria Garages.
> 7.3.1 Garages that are completely separated from the residential
> portion of the building by fire-resistive construction
> sufficient to have them considered separate buildings under
> the local code shall be protected in accordance with NFPA 13.
>
> OK, go to 13...
>
> 8.3.4* Sprinklers shall not be required in garages, open attached
> porches, carports, and similar structures.
>
> Are sprinklers required in the garage or not?
>
>
>
> Vince Sabolik, West Tech Fire Protection, Inc.
> 11351 Pearl Road / Strongsville, Ohio 44136 440 238-4800 Fax 440
> 238-4876
>
>
> ______________________________**_________________
> Sprinklerforum mailing list
>
Sprinklerforum@lists.**firesprinkler.org<[email protected]>
> http://lists.firesprinkler.**org/listinfo.cgi/**
>
sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org