The repeat what John alluded to: 13D is focused solely on life safety (although property protection typically comes along for the ride for MOST fires) as portrayed by the 10 minutes supply. 13R intends a longer duration of life safety and a small bump in property protection with the 30 minute supply and larger design area. IN looking at section 1.2.1 - Purpose for both documents, the term property protection is not in 13D but is in 13R.
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Jun 20, 2013, at 11:41 AM, Vince Sabolik <[email protected]> wrote: > At the risk of sounding even more stupid than I feel, why would > 13D allow ommission of garage heads and 13R not? > > Same situation, the garage is under a room (above) in 13D -or- in 13R, > just an extra story. > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org