What is there to document?
He doesn't understand the Standard;
A fine example of a government employee telling a knowledgeable contractor what 
to do. 

Sent from my iPhone

On Jul 11, 2013, at 4:56 PM, Bobby Gillett <[email protected]> wrote:

> We have a project that requires a Free Standing FDC. Typically we would use
> the scenario of putting the backflow preventer above ground and mounting
> the FDC on the dishcarge side of the backflow before going back
> underground  to supply the system in the building. The local fire marshall
> is wanting the FDC to come off the interior system and pipe underground
> back out to the FDC; he is quoting the explanation after 912.1 of the 2012
> IFC: "These connections give the fire department the capability of
> supplying the necessary water to the automatic sprinkler system at a
> sufficient pressure *without pressurizing the underground supply*."
> I believe this is being misinterpreted - my interpretation is that this is
> referencing *not pressurizing the underground supply* on the supply side of
> the backflow (or a check valve depending on the scenario) - not the
> underground to the system on the discharge side of the backflow.
> 
> Has anyone dealt with this scenario yet and is their documentation out
> there straightening this out?
> 
> Thank you,
> 
> Bobby Gillett
> Living Water Fire Protection, LLC
> (850) 937-1850
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to